SNAP 4-Ch Isolated 5-200 VDC Digital (Discrete) Output Module

Production Specification

The SNAP-ODC5A-i provides four isolated channels of 5-200 VDC digital output, each switching a separate DC load. The module features channel-specific LEDs for troubleshooting and includes a connector clamp to prevent sparks.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

For easier, faster wiring, see SNAP TEX cables and breakout boards.

Build your system in the SNAP I/O Configurator.

 

SNAP-ODC5MA

SNAP-ODC5-i

SNAP-ODC5A-i

SNAP-ODC5ASNK

Key Feature

Diagnostic switches
Four isolated channels

Four isolated channels

Four isolated channels

Load sinking

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

Field Side Ratings (each channel)

Line Voltage - Range

5–60 VDC

5–60 VDC

5–200 VDC

5–200 VDC

Line Voltage - Nominal

5–48 VDC

5–48 VDC

5–200 VDC

5–200 VDC

Current Rating
0 °C to 70 °C Ambient

2 amps per module
0.5 amps per channel

3 amps per module

3 amps per module

3 amps per module

Surge Current

1.5 amps peak for
1 second

5 amps peak for
1 second

5 amps peak for
1 second

5 amps peak for
1 second

Minimum Load

20 mA

20 mA

20 mA

20 mA

Output Voltage Drop

1.6 volts max.@ 0.75 amps

1.6 volts max.@ 0.75 amps

1.6 volts max.@ 0.75 amps

1.6 volts max.@ 0.75 amps

Off-state Leakage

1 mA @ 60 VDC

1 mA @ 60 VDC

1 mA @ 200 VDC

1 mA @ 200 VDC

Peak Blocking Voltage

60 VDC

60 VDC

200 VDC

200 VDC

Fuse
(Common to all Channels)

Has four isolated
channels. User must provide own fusing.

Has four isolated
channels. User must provide own fusing.

Has four isolated
channels. User must provide own fusing.

250 VAC - 4A 5x20 mm
Fast-acting Bell Fuse Part: BEL 5HF4
Opto 22 Part: SNAP-FUSE4AB

Channel-to-channel
isolation

300 VAC
(1500 V transient)

300 VAC
(1500 V transient)

300 VAC
(1500 V transient)

Not applicable

Logic Side Ratings

Pickup Voltage

4 V @ 5.5 mA

4 V @ 5.5 mA

4 V @ 5.5 mA

4 V @ 5.5 mA

Dropout Voltage

1 VDC

1 VDC

1 VDC

1 VDC

Control Resistance

220 ohms

220 ohms

220 ohms

220 ohms

Logic Supply Voltage

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

Logic Supply Current

50 mA maximum

50 mA maximum

50 mA maximum

50 mA maximum

Module Ratings

Number of Channels Per Module

4

4

4

4

Turn-on Time

100 usec

100 usec

100 usec

100 usec

Turn-off Time

750 usec

750 usec

750 usec

750 usec

Isolation (Field Side to Logic Side)

4,000 volts (transient)

4,000 volts (transient)

4,000 volts (transient)

4,000 volts (transient)

Temperature

-20 ° to 70 °C, operating
-40 ° to 85 °C, storage

-20 ° to 70 °C, operating
-40 ° to 85 °C, storage

-20 ° to 70 °C, operating
-40 ° to 85 °C, storage

-20 ° to 70 °C, operating
-40 ° to 85 °C, storage

Wire size range

22 to 14 AWG

22 to 14 AWG

22 to 14 AWG

22 to 14 AWG

Agency Approvals

UL, CE, RoHS, DFARS; UKCA

UL, CE, RoHS, DFARS; UKCA

UL, CE, RoHS, DFARS; UKCA

UL, CE, RoHS, DFARS; UKCA

Warranty

30 months

Lifetime

Lifetime

Lifetime

SNAP Digital Output Modules Data Sheet

Opto 22 SNAP digital output modules are designed to mount on SNAP PAC racks and be used with SNAP PAC brains and R-series controllers, both standard wired and Wired+Wireless models. You can choose from AC or DC output modules.

These modules are also compatible with SNAP D-series and legacy M-series and B-series racks, and they can be used with legacy Ethernet-based brains as well as other SNAP brains, such as the serial B3000 or the B3000-HA.

This data sheet covers the following part numbers:
SNAP-OAC5
SNAP-OAC5-I
SNAP-OAC5MA
SNAP-ODC5A-I
SNAP-ODC5ASNK
SNAP-ODC5-I
SNAP-ODC5MA
SNAP-ODC5SNK
SNAP-ODC5SRC
 

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

Digital I/O for Raspberry Pi Selection Guide

Now you can safely and reliably sense and switch industrial-level electrical loads with your Raspberry Pi® and Opto 22 industrially hardened digital I/O.

This Selection Guide describes compatible I/O racks and modules, power supplies, and accessories that work with the Raspberry Pi and the Digital I/O Carrier Board for the Pi (OPTO-P1-40P). Specifications, dimensional drawings, and wiring diagrams for racks and I/O modules are included.

For code samples and steps to get started, also see developer.opto22.com.

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Sinking or Sourcing Technical Note

View this technical note on a web page.

Are you confused about sinking and sourcing when wiring DC circuits? This technical note explains what sinking and sourcing mean, explores where you would use one wiring method rather than the other, and shows how to use a discrete output module with your DC circuit.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

CAD 3D Drawing: SNAP-ODC5A-I Digital Output Module

This CAD file contains a 3-dimensional drawing of the SNAP-ODC5A-I digital output module, which provides four isolated channels of 5-200 VDC digital output, each switching a separate DC load. 

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.

Video: Securing SNAP Module

A quick overview on securing a SNAP Module to a SNAP rack.

Video: Removing a SNAP Module

A quick overview on removing a SNAP module.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.