SNAP-AOV-25
Hover over image to zoom in

$425.00 (USA and Canada only)

Availability: In stock
SNAP 2-Ch 0-10 VDC Analog Voltage Output Module

Production Specification

The SNAP-AOV-25 provides two channels of analog voltage output at a nominal range of 0-10 volts. Each channel can supply +5 mA of load current. Although the two channels are not isolated from each other, the module is transformer isolated and optically isolated from other modules and devices. The module is factory calibrated.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

Input

12-bit serial data
(each channel)

Outputs

0 to +10 Volts DC

Span

10 Volts

Resolution

2.44 mV

Response Time
(% of span/delta V/delta time)

99.9%/19.98 V/3 mS

DC Common Mode Rejection

>-120 dB

AC Common Mode Rejection

>-120 dB @ 60 Hz

Maximum Operating Common Mode Voltage

250 V

Common Mode Resistance

>1,000 Megohms

Load Current (nominal)

5 mA (each channel)

Short Circuit Output Current Continu­ous

40 mA per channel

Accuracy

0.1% of Span

Gain Temperature Coefficient

50 PPM/°C

Offset Temperature Coefficient

20 PPM/°C

Isolation

1500 V

Power Requirements

5 Volts DC (±0.15) @ 150 mA

Ambient Temperature:
Operating
Storage

 

-20 °C to 70 °C
-40 °C to 85 °C

Humidity

5-95%, non-condensing

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

Wire size range

22 to 14 AWG

Agency Approvals

UL, CE, RoHS, DFARS; UKCA, NEBS

Warranty

Lifetime

SNAP Analog Output Modules Data Sheet

SNAP I/O analog output modules are part of Opto 22's SNAP PAC System. This document includes descriptions, specifications, and wiring and dimensional diagrams for all SNAP analog output modules:

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Case Study: University of California, Irvine

At the University of California, Irvine, Scientist Dr. John Garman and a team of his engineering students use an Opto 22 SNAP PAC System in their research of coal and biomass combustion. The SNAP PAC hardware controls the coal feed rate into an entrained flow reactor, monitors thermocouples that feed back process control data, monitors emissions, and acquires and logs data on operating conditions within the reactor.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.

Video: Securing SNAP Module

A quick overview on securing a SNAP Module to a SNAP rack.

Video: Removing a SNAP Module

A quick overview on removing a SNAP module.

Video: Automation 101: Wire a Valve Actuator

Learn how you can wire a valve actuator to control amount of heating and cooling water flow in a HVAC system.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.