SNAP 1-Ch 4-20 mA Current Loop Analog Output Module

Production Specification

The SNAP-AOA-3 provides a single channel of digital-to-analog conversion. The module has a true differential (floating) output that eliminates ground loops and has a nominal output range of 4-20 mA. The module is transformer isolated and optically isolated from other modules and devices, and is factory calibrated.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

For a similar module with two channels, see SNAP-AOA-23.

Input

12-bit serial data

Output

4 to 20 mA (floating)

Span

16 mA

Resolution

3.9 microamps

Response Time
(% of span/delta I/ delta time)

99.9%/15.98 mA/3 mS

DC Common Mode Rejection

>-120 dB

AC Common Mode Rejection

>-120 dB @ 60 Hz

Maximum Operating Common Mode Voltage

250 V

Common Mode Resistance

>1000 M W

Accuracy

0.1% of span

Gain Temperature Coefficient

50 PPM/ °C

Offset Temperature Coefficient

20 PPM/ °C

Module Power Requirements

5 Volts DC (±0.15 ) @ 140 mA

Loop Power Requirements

10 Volts DC (min) to
32 Volts DC (max)

Max. Loop Resistance
(Ohms)
@ Loop Supply

 

250
10V

 

350
12V

 

950
24V

 

1350
32V

Max. Loop Resistance formula

(Loop Voltage - 5)
0.02

Ambient Temperature:
Operating
Storage

 

-20 °C to 70 °C
-40 °C to 85 °C

Humidity

5-95%, non-condensing

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

Wire size range

22 to 14 AWG

Agency Approvals

UL, CE, RoHS, DFARS; UKCA

Warranty

Lifetime

SNAP Analog Output Modules Data Sheet

SNAP I/O analog output modules are part of Opto 22's SNAP PAC System. This document includes descriptions, specifications, and wiring and dimensional diagrams for all SNAP analog output modules:

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.