SNAP 8-ch analog multifunction output, voltage or current

Production Specification

The SNAP-AOVA-8 analog output module has 8 channels, each individually configurable for any one of six voltage or current output ranges.

Voltage:
0 to 5 VDC
0 to 10 VDC
-5 to +5 VDC
-10 to +10 VDC

Current:
4 to 20 mA
0 to 20 mA

The SNAP-AOVA-8 requires a 24 VDC excitation voltage brought in through the field connector on the top of the module. This voltage is internally isolated with transformer and digital data isolators, and then used to source all channels.

Because all current is sourced from within the module using the 24 VDC excitation, current outputs cannot be used with an external loop supply. Current outputs are self-sourcing and cannot be used in loops that are loop-powered or already have a self-sourcing device in the loop.

The SNAP-AOVA-8 mounts on a SNAP PAC rack alongside other I/O modules (digital, analog, and serial). This module requires a SNAP PAC brain or rack-mounted controller with firmware version R9.4b or higher. It cannot be used with legacy controllers or brains.

To wire the module, a 6-foot-long SNAP-HD-20F6 cable is required. The cable has a 20-pin connector at the module end and flying leads for wiring to field devices.

Excitation Range

18 TO 32 VDC

Excitation Current Required

200mA @ 32VDC, 250mA @ 24VDC, 350mA @ 18VDC

24V Excitation Fault Recovery Time

15 mS nominal

Power Requirement (from the rack)

5 VDC (±0.15) @ 150 mA

Maximum Operating Common Mode Voltage

250 volts

Isolation

1500 V (transient)

DC Common Mode Rejection

>-120 dB

AC Common Mode Rejection

>-120 dB @ 60 Hz

Data Refresh Time

9 mS nom (update 1 ch/ms)

Ambient Temperature:
 Operating
 Storage

 

-20 to 70 °C
-40 °C to 85 °C

Humidity

 

5-95%, non-condensing

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

Wire size range

22 to 14 AWG

Agency Approvals

UL, CE, RoHS, DFARS; UKCA

Warranty

Lifetime

Voltage Outputs

Output Range (Resolution)

0 to 5 VDC (1.22 mV)
0 to 10 VDC (2.44 mV)
-5 to +5 VDC (2.44 mV)
-10 to +10 VDC (4.88 mV)

Load Current

+/-10 mA min. each voltage output channel)

Short Circuit Current

16 mA Typ.

Accuracy

0.1% of span

Drift:
Gain Temperature Coefficient
Offset Temperature Coefficient

 

30 PPM / °C
15 PPM / °C

Current Outputs

Output Range (Resolution)

4 to 20 mA (4 microamps)
0 to 20 mA (5 microamps)

Maximum Loop Resistance

750 Ohms (each current out­put channel )

Open Circuit Volts

27 VDC max.
(24 VDC typical)

Accuracy

0.1% of span

Drift:
Gain Temperature Coefficient
Offset Temperature Coefficient

 

30 PPM / °C
15 PPM / °C

SNAP Analog Output Modules Data Sheet

SNAP I/O analog output modules are part of Opto 22's SNAP PAC System. This document includes descriptions, specifications, and wiring and dimensional diagrams for all SNAP analog output modules:

SNAP PAC System Specification Guide

This guide is a comprehensive introduction to the SNAP PAC System. The guide describes the system's components (software, controllers, I/O processors, and I/O); shows how to build a basic system and how to expand it; and includes installation instructions, wiring diagrams, dimensional drawings, and specifications for parts.

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

SNAP I/O Modules Firmware Release Notes

This document lists the latest updates to the firmware for SNAP I/O modules. It includes information on new features, enhancements, and bug fixes.

List of SNAP I/O module firmware download pages

Note: This document was formerly called a readme. The name was changed to more accurately describe its content.

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

SNAP-AOVA-8 Module Firmware

This download contains current firmware for the SNAP-AOVA-8 multifunction (voltage or current) analog output module.

For a list of bug fixes and enhancements included in this firmware, see the SNAP I/O Modules Firmware Release Notes.
 

CAD 3D Drawing: SNAP-AOVA-8 Analog Output Module

This file contains a 3-dimensional CAD drawing of the SNAP-AOVA-8 analog output module. This module provides 8 channels, each individually configurable for any one of six voltage or current output ranges.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.