P240D4-17
Hover over image to zoom in

Availability: Obsolete
OBSOLETE P Model, 240 VAC, 4 Amp, DC Control Solid State Relay (SSR), Replacement Part Only

Production Specification

*** NOTE: This part is OBSOLETE and no longer available. ***
Please consider contact Opto 22 Pre-Sales engineers for more information.

This P Model, 240 VAC, 4 Amp, DC Control Solid State Relay (SSR) should be used as a replacement part only. For new development, use the equivalent P240D4 SSR instead. The two parts are manufactured identically using the same VDE-approved optocoupler and have identical specifications.

Lots of information on choosing and using SSRs can be found in the SSR data sheet. Also see the Manufacturers' part number cross-reference list.

NOTE: Specifications for P240D4-17 are identical to P240D4.

120/240 Volt Solid State Relays

 

MP120D2
or P120D2

MP120D4
or P120D4

MP240D2
or P240D2

MP240D4
or P240D4

MP380D4

Nominal AC Line Voltage

120

120

240

240

380

Nominal Current Rating Amps

2

4

2

4

4

1 cycle Surge (Amps) Peak

20

85

20

85

85

Nominal Signal Input
Resistance (Ohms)

1000

1000

1000

1000

1000

Signal Pick-up Voltage

3VDC***
(24V allowed)

3VDC***
(24V allowed)

3VDC***
(24V allowed)

3VDC***
(24V allowed)

3VDC***
(24V allowed)

Signal Drop-out Voltage

1 VDC

1 VDC

1 VDC

1 VDC

1 VDC

Peak Repetitive Voltage Maximum

600

600

600

600

800

Maximum Output Voltage Drop

1.6 volts

1.6 volts

1.6 volts

1.6 volts

1.6 volts

Off-State Leakage mA Maximum**

5 mA

5 mA

5 mA

5 mA

5 mA

Operating Voltage Range (Volts AC)

12–140

12–140

24–280

24–280

24–420

I2t Rating t=8.3 (ms)

2

30

2

30

30

Isolation Voltage

4,000 VRMS

4,000 VRMS

4,000 VRMS

4,000 VRMS

4,000 VRMS

θjc* °C/Watt

20

6.5

20

6.5

6.5

Dissipation Watts/Amp

1.2

1.2

1.2

1.2

1.2

Rating (Motor Load)

1 FLA at 120 VAC
6 LRA at 120 VAC

2.5 FLA at 240 VAC
6 LRA at 240 VAC

1 FLA at 120 VAC
15 LRA at 120 VAC

2.5 FLA at 240 VAC
15 LRA at 240 VAC

2.5 FLA at 380 VAC
15 LRA at 380 VAC

Agency Approvals UL, CSA, RoHS, CE; UKCA UL, CSA, RoHS, CE; UKCA UL, CSA, RoHS, CE; UKCA UL, CSA, RoHS, CE; UKCA UL, CSA, RoHS, CE; UKCA

Notes: θjc* = Thermal resistance junction to base. Maximum junction temperature is 110 °C.
** Operating Frequency: 25 to 65 Hz (operates at 400 Hz with 6 times the offstate leakage)
*** = P Series 32 volts maximum.

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

CSA Approval Document

This document lists all Opto 22 part numbers that have the Canadian Standards Association (CSA) approval.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

No downloads are available for this product.
No videos or demos are available for this product.