KB90799
Published: December 7, 2023
GRV-IDCIFQ-12 module with channel configured as quadrature with index: occasionally, index doesn't update
Firmware for the GRV-IDCIFQ-12 module
All versions prior to R1.3e
R1.3e
Note: This issue applies only to users who configure their modules through OptoMMP. It does not apply to PAC Control or CODESYS users.
If a GRV-IDCIFQ-12 module has a channel configured as quadrature with index, occasionally, the index may not update. The following table illustrates how this issue may affect counter values.
Previous 3 values |
Current value |
Value after 1 pulse
(expected result) |
Value after 1 pulse
(results with this issue) |
Channel 0, configured as a counter; measures number of pulses |
...36...37...38... |
39 |
...40 |
...40 |
Channel 1, configured as a counter; measures number of pulses since last index |
...16...17...18... |
19 |
...0 |
...0 |
Channel 2, configured as a quadrature counter with index; measures index |
...20...20...20... |
20 |
...40 |
...20 |
In your programming logic, verify the index value by comparing the number of pulses since the last index (in the above example, that would be the value provided in channel 2) to the index value. If the index value does not match, add one full rotation of pulses.