KB90735
Published: October 2, 2023
PID output may not be set to forced output value
Firmware for the following:
  • SNAP-PAC-EB1, SNAP-PAC-EB1-FM, SNAP-PAC-EB1-W
  • SNAP-PAC-EB2, SNAP-PAC-EB2-FM, SNAP-PAC-EB2-W
  • SNAP-PAC-SB1, SNAP-PAC-SB2
All versions prior to R10.4e
R10.4e
Under the following circumstances, a PID output may not be set to the value specified in the "Force output when input goes out of range" field:
  • The input matches the Out Of Range Value (16-bit) on the PAC Manager Status Write page.
    Note: The default value for the Out of Range Value is -32768.
  • The Max Change value must be non-zero
  • The current PID output value must be greater than the sum of the "Max Change" and forced output values
Add a chart that monitors the PID's input and output values, then switches the PID to manual mode and sets its output to one of the "force" values.