KB89087
Published: July 22, 2020
Quadrature Counter Feature Not Set on GRV-IDCIFQ-12 Module
Firmware for GRV-EPIC-PR1
All versions prior to 2.0.2
2.0.2
In a PAC Control strategy, if you add a GRV-IDCIFQ-12 module to an EPIC I/O unit, and add a channel on the module with the Quadrature Counter feature, the feature is not set on the EPIC I/O unit. When you check the channel on the I/O unit with groov Manage, the channel will indicate that no feature is set.
To check the channel through groov Manage:
  1. Log into your GRV-EPIC-PR1 with a user ID that has system-level privileges.
  2. From the groov Manage Home page, click I/O.
  3. From the Modules page, click on the GRV-IDCIFQ-12 module.
  4. From the Module page, click on the channel you configured with the Quadrature Counter feature.