KB89084
Published: September 18, 2020
I/O configuration between PAC Control and groov RIO do not match; -56 "Invalid Address" error
GRV-R7-MM1001-10
2.0.0 to 2.0.1
2.0.2
If you have "Watchdog timeout after <x> second(s) of no communications" enabled for a groov RIO I/O unit in your PAC Control strategy, when you go into Debug mode and run your strategy, you may see the following:
- Error code -56 "Invalid Address" for chart <system: _INIT_IO> in the controller's message queue.
- When you check the I/O configuration in groov Manage (from groov Manage Home, click I/O Channels, then the channel number), it does not match the I/O configuration in PAC Control.
Do not enable communications watchdog from within PAC Control (through the Edit I/O Unit window). Instead, after you download and run the strategy, enable the communication watchdog in groov Manage:
- On the groov RIO, log in with a user ID that has administrator privileges.
- From the groov Manage Home page, click I/O Config.
- Enter a value in the Watchdog Timeout (ms) field.
- Click Save.