KB88647
Published: November 14, 2019
PID loops configured for Auto mode may start in Manual mode (or vice versa)
Firmware for:
  • GRV-EPIC-PR1
  • SNAP-PAC-S2, SNAP-PAC-S2-W
  • SoftPAC
  • SNAP PAC Sim Control Engine Simulator
R10.0a - R10.0f for SNAP PAC controllers
All versions for GRV-EPIC-PR1
R10.0h for SNAP PAC controllers
If a PAC Control strategy has PID loops configured with Mode set to Auto, when you run the strategy, the PID may start in Manual mode (or vice versa). In addition, the Get PID Mode command may return a value other than 0 (Auto) or 1 (Manual); a non-zero value indicates Manual mode.
Modify the PAC Control strategy and add the Set PID Mode command in the Powerup chart to set the desired PID mode.