KB91189
Published: May 31, 2025
CODESYS licenses missing after installing firmware
- GRV-EPIC-PR1
- GRV-EPIC-PR2
groov RIOs:
- GRV-R7-MM1001-10
- GRV-R7-MM2001-10
- GRV-R7-I1VAPM-3
3.6.0 to current
This KB article describes an issue that affects CODESYS users. It occurs when your groov EPIC or RIO has firmware 3.6.x, and then you install any firmware version.
If your groov EPIC or RIO already has firmware version 3.6.x and then you install any firmware version (including the same version), when you start CODESYS and check License Manager, you’ll see that the licenses are gone. The firmware update should have preserved the licenses.
Running 3.6.x and Have NOT Installed or Updated Firmware or Performed a Reset to Factory Defaults
If your EPIC or RIO already has firmware version 3.6.x with CODESYS licenses installed, back up the licenses before you install any firmware version (including the same version) or perform a Reset to Factory Defaults:
- In CODESYS Development System, open the project that runs on your device (EPIC or RIO), connect to the device, and copy the license files stored in the device to a safe location on your computer. The license files are located in the cmact_licenses folder. For instructions on copying license files stored in your device, refer to "Backing up and Restoring CODESYS Licenses" topic in CODESYS online documentation.
- Install your desired version of groov EPIC or RIO firmware. For instructions, refer to the appropriate form:
- In groov Manage, enable the CODESYS controller:
- From the groov Manage Home page, click Controller > CODESYS Controller (groov EPIC) or Controller (groov RIO).
- Click Enable. Click OK on the warning message.
- In CODESYS Development System, copy the license files you saved in step 1 back to the groov EPIC or groov RIO. For instructions on copying license files to your device, refer to "Backing up and Restoring CODESYS Licenses" topic in CODESYS online documentation.
- Using groov Manage, do one of the following:
- Disable then enable the CODESYS controller:
- Click Disable. Click OK on the warning message.
- When the Status field shows Disabled, click Enable. Click OK on the warning message.
- Restart your groov EPIC:
- From the groov Manage Home page, click System > Restart.
- Click Restart on the prompt.
- Click Close on the success prompt. Wait for approximately five minutes (groov EPIC) or 10 minutes (groov RIO) for the restart to complete. If the page does not refresh on its own, manually refresh the browser.
- In CODESYS Development System, use the License Manager to confirm that the license has been restored. For instructions on using the License Manager, refer to the “Licensing the Controller” topic in the CODESYS online documentation.
Running 3.6.x and Already Updated or Installed Firmware or Performed a Reset to Factory Defaults
If your
groov EPIC or RIO had firmware version 3.6.x with CODESYS licenses installed, and then you installed any firmware version (including the same version) or performed a Reset to Factory Defaults, the CODESYS licenses were not restored to your EPIC or RIO. You will need to restore the licenses, but the procedure depends on the firmware version running on your EPIC or RIO when you first installed the licenses:
- If you first installed the CODESYS license in firmware version 3.4.5 or lower and have already installed version 4.0.x (or reinstalled 3.6.x) or higher:
- Install firmware version 3.4.5 (or lower). For instructions, refer to the appropriate form:
- In CODESYS Development System, restore the CODESYS licenses using the License Manager. For instructions on using the License Manager, refer to the “Licensing the Controller” topic in the CODESYS online documentation.
- Install firmware version 4.0.x or higher. Do not install version 3.6.x. For instructions, refer to the appropriate form:
- In CODESYS Development System, use the License Manager to confirm that the licenses have been restored.
- If you first installed the CODESYS license in firmware version 3.5.x or 3.6.x, and have already installed version 4.0.x (or reinstalled 3.6.x) or higher:
- In CODESYS Development System, restore the CODESYS license using the License Manager. For instructions on using the License Manager, refer to the “Licensing the Controller” topic in the CODESYS online documentation.
- Use the License Manager to confirm that the license has been restored.
Follow the instructions in the Workaround.
Copyright © 2025 Opto 22. All rights reserved.