KB90892
Published: June 17, 2024
Data Services OPC UA server may not report new values after PAC Control strategy download or I/O reconfiguration
  • GRV-EPIC-PR1
  • GRV-EPIC-PR2
  • GRV-R7-MM1001-10
  • GRV-R7-MM2001-10
  • GRV-R7-I1VAPM-3
For groov EPICs: 3.4.0 to 3.5.1
For groov RIOs: 3.4.0 to 3.5.0
For groov EPICs: 3.6.0
For groov RIOs: 3.6.0
After either of the following situations, you may observe—in your OPC UA client—that data reported by the Data Services OPC UA server remains the same, even though you can observe a change through other methods (for example, the PAC Control debugger):
  • Downloading a PAC Control strategy on a groov EPIC.
  • Reconfiguring I/O or modifying Scratchpad values on either a groov EPIC or a groov RIO.
After downloading a PAC Control strategy on a groov EPIC or reconfiguring I/O on either a groov EPIC or a groov RIO, restart the Data Service:
  1. Log into your groov EPIC or groov RIO with an ID that has system administrator permission.
  2. From the groov Manage Home page, click Data Services.
  3. In the Status section, click Disable on the Data Service Runtime field.
  4. After the Data Service field changes to Disabled, click Enable. Wait for the Data Service field to change to Running.