KB90508
Published: May 3, 2023
I/O Services may become unresponsive upon startup or after installing a GRV-IVAPM-3 module
Firmware for the following:
- GRV-EPIC-PR1
- GRV-EPIC-PR2
1.4.3 to 3.4.4
3.4.5
You may have this issue if you observe the following:
- Functions on the I/O Services page (from the groov Manage Home page, click I/O > I/O Services) do not work correctly.
- No responses from the memory map nor the I/O.
- On groov Manage I/O page (from the groov Manage Home page, click I/O), there is a yellow banner at the top with the message "I/O offline" and no modules are listed in the slots.
- Some module LEDs turn red.
This is more likely to happen in the following situations:
- At start up.
- When you install a GRV-IVAPM-3 module on the chassis.
- You hot swap a GRV-IVAPM-3 module into a slot previously unoccupied or occupied by a module of a different type.
There may not be any messages in the I/O Services log file to indicate that there may be an issue.