KB90249
Published: November 18, 2022
Importing chart may cause PAC Control to crash
- PAC Control Professional
- PAC Control Basic
All versions prior to R10.5a
R10.5a
On rare occasions, when you import a chart into a PAC Control strategy, if the I/O of the chart being imported does not match the I/O of the strategy, PAC Control may crash. If the chart imports successfully, the strategy may not compile or it may crash when you select Tools > Regenerate Reference Counts.
Conditions for the issue to occur:
- I/O points are SNAP or groov (G4 is not affected).
- The I/O point being imported is on an I/O unit with the same name as an I/O unit in the target strategy.
- There is already an I/O point configured in the same point location in the target strategy, but the point name is different.
Follow these steps to work around the issue:
- Create a new strategy.
- Import the chart into the new strategy. This helps you see the I/O units and channels that are referenced in the chart being imported.
- Compare the I/O modules and channels of the new strategy with the target strategy (the strategy you want to import the chart into).
- Modify the target strategy to eliminate the conditions mentioned above and then save the target strategy.
- Export the chart from the new strategy.
- Import the chart into the target strategy.
- Save the target strategy.
- Select Tools > Regenerate Regenerate Reference counts.
- Select Compile > Compile All.