KB89950
Published: November 2, 2021
For temperature input channel types, calibration offset parameter may be applied incorrectly
  • GRV-EPIC-PR1
  • GRV-EPIC-PR2
3.2.1 to 3.2.2
3.3.0
For groov EPIC I/O units configured with a groov I/O module that reads temperatures, if you set a non-zero value for the calibration offset for a channel and then reset the module or I/O unit, the value applied by the channel for calibration offset may be incorrect. The value applied depends on how the I/O unit was configured and changed:
  • If you configured the I/O unit for °F, then you entered a non-zero value for the offset, then reset the module or I/O unit, the calibration offset value reported by the channel is 9/5ths greater than what you entered.
  • If the I/O unit was configured for °F, then you entered a non-zero value for the offset, then you switched the I/O unit to °C, then reset the module or I/O unit, the calibration offset value reported by the channel is the same as what you entered. This is incorrect; it should be 5/9ths smaller than what you entered.
  • If the I/O unit was configured for °C, then you entered a non-zero value for the offset, then you switched the I/O unit to °F, then reset the module or I/O unit, the calibration offset value reported by the channel is the same as what you entered. This is incorrect; it should be 9/5ths larger than what you entered.
IMPORTANT: After you upgrade the firmware to version 3.3.0, which fixes this issue, you will need apply the correct calibration offset to the temperature input channels affected by this issue.
Configure the I/O Unit for Celsius Temperature Unit. Set the desired calibration offset in Celsius for the temperature input channel then click save. Now the I/O Unit Temperature Unit can be set to Fahrenheit, if desired, and the values will be correct after a reset.