KB89735
Published: March 9, 2022
Control engine resets on first attempt to communicate with an alternate host task
Firmware for the following groov EPIC processors:
- GRV-EPIC-PR1
- GRV-EPIC-PR2
Firmware for SoftPAC
For listed groov EPICs: 2.0.1 to 3.2.0
For SoftPAC: 10.3b to R10.4c
For listed groov EPICs: 3.2.1
For SoftPAC: R10.4d
After you do the following steps, the groov EPIC control engine resets; for SoftPAC, a -16 bus error message is placed in its message queue and the alternate host task will not work:
- In a PAC Control strategy, use an extended bank write command, such as Move Numeric Table To I/O Unit Ex, with over 16 channels per module for a groov EPIC or a groov RIO I/O unit. The I/O unit must contain at least one configured analog output channel.
- Start an alternate host task.