KB89620
Published: January 31, 2022
Debug mode reports incorrect point type on E2 I/O units
  • PAC Control Basic
  • PAC Control Pro
R10.3a to R10.4a (may occur in earlier versions)
R10.4b
In the following situation, PAC Control reports an incorrect point type and value for a point on an E2 I/O unit:
  1. In PAC Control Config mode, modify the point type of a point on an E2 I/O unit.
  2. Switch to Debug mode.
  3. View the point's point type and value. The type will be the type before you modified it in step 1 and the value will be incorrect.
Delete the point and create a new one. One way to do this is to use the Find/Replace feature in PAC Control:
  1. Create a new point with a similar name and the correct type and feature on an unused position on the E2 I/O unit. If there are no empty positions available, create a new E2 I/O Unit and create the point on the new I/O unit.
  2. Use Find/Replace to move all strategy references from the corrupt point to the new point.
    1. Click Edit > Replace.
    2. In the Find What field, select the corrupt point.
    3. In the Replace With field, select the new point.
    4. Click Replace All.
  3. Regenerate reference counts and save the strategy.
    1. Click Tools > Regenerate Reference Counts.
    2. Click File > Save Strategy.
  4. Delete the corrupt point by right-clicking on the name of the point in the Strategy tree, then selecting Delete.
  5. Save the strategy by clicking File > Save.
  6. Rename the new point to the name of the now-deleted corrupt point, then move it to the old position:
    1. Double-click the name of the new point in the Strategy tree.
    2. Type in the name of the now-deleted corrupt point in the Name field, then click OK.
    3. Right-click on the point's name and select Configure.
    4. In the Configure I/O Points dialog, select the point's name and click Move to.
    5. In the Move Point dialog, select the module and position where the now-deleted corrupt point was located.
    6. Click OK.
  7. Save the strategy.