Timeout or "The secure channel has been closed" error while browsing static tags on a CODESYS OPC UA server
groov View running on:
  • GROOV-AT1, GROOV-AT1-SNAP
  • GRV-EPIC-PR1
GRV-EPIC-PR1: 3.1.0 to current
All other products: R4.3a to current
While browsing static tags on a CODESYS OPC UA server, including the one in the GRV-EPIC-PR1, groov View reports a timeout or displays the message The secure channel has been closed. After that, any attempt to communicate with that CODESYS server will fail.
If you review the logs, you may see messages like the following:
19:45:32,827 WARN  [qtp1965237677-19] c.o.g.s.d.o.OpcUaStaticTagBrowser - Could not browse OPC UA node.
com.prosysopc.ua.ServiceException: Bad_SecureChannelClosed (code=0x80860000, description="The secure channel has been closed.")
19:46:32,847 WARN  [PublishTask-com.opto22.groov.server.opcua.OpcUaClientEx@39afdd2] o.o.u.t.t.i.SecureChannelTcp - Connection failed: Bad_CommunicationError (code=0x80050000, description="2147811328, Read timed out")
19:46:32,847 WARN  [PublishTask-com.opto22.groov.server.opcua.OpcUaClientEx@39afdd2] o.o.u.t.t.i.SecureChannelTcp - Bad_CommunicationError: Retrying
19:48:34,113 WARN  [PublishTask-com.opto22.groov.server.opcua.OpcUaClientEx@39afdd2] o.o.u.t.t.i.SecureChannelTcp - Connection failed: Bad_CommunicationError (code=0x80050000, description="2147811328, Read timed out")
19:48:34,113 WARN  [PublishTask-com.opto22.groov.server.opcua.OpcUaClientEx@39afdd2] o.o.u.t.t.i.SecureChannelTcp - Bad_CommunicationError: Retrying
19:48:55,196 WARN  [qtp1965237677-19] c.o.g.s.d.o.OpcUaStaticTagBrowser - Could not connect to OPC UA server.
19:50:35,307 WARN  [qtp1965237677-37] o.o.u.t.t.i.SecureChannelTcp - Connection failed: Bad_CommunicationError (code=0x80050000, description="2147811328, Read timed out")
19:50:35,307 WARN  [qtp1965237677-37] o.o.u.t.t.i.SecureChannelTcp - Bad_CommunicationError: Retrying
19:51:36,469 WARN  [qtp1965237677-37] c.o.g.s.d.o.OpcUaStaticTagBrowser - Could not connect to OPC UA server. Failed to create secure channel to server: : opc.tcp://codesys1:4840 [http://opcfoundation.org/UA/SecurityPolicy#None,None]
​Note that these messages may also indicate that you configured the CODESYS OPC UA  device with the wrong address. Double check that your configuration details are correct, and, if possible, try using another OPC UA client to verify the address.
To re-establish communication to the CODESYS OPC UA server, restart the GRV-EPIC-PR1.