KB89073
Published: July 22, 2020
If RIO Channels Changed from One Supported Combination to Another Supported Combination, Errors may be Reported
Firmware for:
For GRV-EPIC-PR1 Firmware: All versions prior to 2.0.2For SoftPAC Firmware: R10.3a to current
For GRV-EPIC-PR1 Firmware: 2.0.2For SoftPAC Firmware: R10.3b
On a GRV-R7-MM1001-10, channels 0-3 cannot combine discrete sinking outputs with thermocouple inputs. In PAC Control, if you:
- download and run a strategy that configures channels 0-3 with one valid combination (for example, all of them are 5-30 VDC Digital Output), and then
- modify the strategy to configure channels 0-3 to another valid combination (for example, all of them are Type J Thermocouple),
when you download the modified strategy, you may see one or more "I/O point mismatch" errors in the controller's message queue and your I/O configuration may end up as one of the following:
- Same as the combination specified in the original strategy.
- Different from the original strategy but not as specified in the modified strategy.
Workaround through a combination of groov Manage and PAC Control
- Log into your GRV-R7-MM1001-10 with a user ID that has administrator privileges.
- From the groov Manage Home page, click I/O Config, then click Reset I/O to Defaults to clear the I/O configuration.
- In PAC Control, download and run strategy with the desired configuration.
Workaround through only PAC Control
- Create a strategy that configures channels 0-3 as digital inputs.
- Switch to Debug mode. If PAC Control displays the Download Warning - Strategy Mismatch window, click Yes.
- Run the strategy.
- Switch back to Config mode.
- Open the strategy with the desired configuration.
- Run the strategy.