KB88962
Published: July 21, 2021
Revision: 4.0
TPO Channel's State Does Not Change With Percentage (Duty Cycle) of 100%, 0%, or Less Than 0%
Firmware for:
  • GRV-R7-MM1001-10
  • GRV-ODCSRC-24
  • GRV-ODCI-12
  • GRV-OAC-12
  • GRV-OACI-12
GRV-OAC-12, GRV-OACI-12: R1.3b
GRV-ODCSRC-24, GRV-ODCI-12: 1.3c
GRV-R7-MM1001-10: All versions prior to 3.0.0
GRV-OAC-12, GRV-OACI-12: R1.3c
GRV-ODCSRC-24, GRV-ODCI-12: 1.3d
GRV-R7-MM1001-10: 3.0.0
In a PAC Control strategy with either:
  • a GRV-EPIC-PR1 I/O unit that has any of the listed groov I/O modules with a digital output channel configured as TPO, or
  • a GRV-R7-MM1001-10 I/O unit that has a digital output channel configured as a TPO,
you may observe any of the following:
  • Scenario 1:
    1. Set the TPO channel constantly off with the Turn Off command.
    2. Configure the TPO's period to a desired period with the Set TPO Period command.
    3. Set the TPO's duty cycle to 100% with the Set TPO Percent command.
    4. Observe the TPO channel's output. The TPO channel's output will remain off, but it should be constantly on.
  • Scenario 2:
    1. Set the TPO channel constantly on with the Turn On command.
    3. Set the TPO's duty cycle to 0% or less (such as -50%) with the Set TPO Percent command.
    4. Observe the TPO channel's output. The TPO channel's output will remain on, but it should be constantly off.
Instead of setting the TPO percent to 100% to set the TPO channel constantly on, use the "Turn On" command.
Instead of setting the TPO percent to 0% or less to set the TPO channel constantly off, use the "Turn Off" command.