KB88826
Published: December 9, 2020
Output of TPO with Percentage (Duty Cycle) Above 100% is Not Constantly On
Firmware for:
- GRV-EPIC-PR1
- GRV-R7-MM1001-10
GRV-EPIC-PR1: All versions prior to 3.0.0GRV-R7-MM1001-10: All versions prior to 3.0.0
GRV-EPIC-PR1: 3.0.0GRV-R7-MM1001-10: 3.0.0
You may observe this issue on a GRV-R7-MM1001-10 or a GRV-EPIC-PR1 with any of the following I/O modules:
- GRV-ODCSRC-24
- GRV-ODCI-12
- GRV-OAC-12
- GRV-OACI-12
After setting the TPO's percentage (duty cycle) above 100%, you may see either of the following behaviors on the TPO digital output point:
- Turns off and remains off.
- Turns off after a short delay and occasionally turns on briefly before turning back off (behavior similar to a TPO with a small duty cycle). The duration of the on-time is dependent on the TPO's period and percentage.
The following examples show the incorrect behavior you may observe with specific values for period and percentage:
- If you set a TPO with a 200% duty cycle:
- If the TPO's period is 0.5 s, then the on-time is about 1 s and off-time is about 214.25 s.
- If the TPO's period is 0.05 s, then the on-time is about 0.1 s and off-time is about 214.7 s.
- If the TPO's period is 0.005 s, then the on-time is about 0.01 s and off-time is about 214.75 s.
- If you set a TPO with a 101% duty cycle:
- If the TPO's period is 0.5 s, then the on-time is about 0.5 s and the off-time is about 214.746 s.
- If the TPO's period is 0.005 s, then the on-time is about 0.0055 s and off-time is about 214.748 s.
- If the TPO's period is 0.05 s, then the TPO channel's output remains off with no on-time.
Do not set a TPO with a percentage (duty cycle) above 100%.