KB88545
Published: October 14, 2019
Tags are not refreshed correctly after a restart
Opto 22 groov EPIC and SNAP PAC Driver module, available from Cirrus Link website and also delivered in firmware for GRV-EPIC-PR1
3.3.0-3.4.7, 4.0.0-4.0.1 of Opto 22 groov EPIC and SNAP PAC Driver module
Al versions prior to 1.4.3 of GRV-EPIC-PR1
3.4.8 of Opto 22 groov EPIC and SNAP PAC Driver module
4.0.2 of Opto 22 groov EPIC and SNAP PAC Driver module
When you work with Ignition or Ignition Designer and the Opto 22 groov EPIC and  SNAP PAC Driver module, when tag lists are restored after any of the following events, some of the OPC-UA tags may appear valid but are not updated with current controller values. Strings will be blank and numeric tags will be 0. When scanned values change in the controller, their values update the OPC-UA tag.
Events that may trigger this issue include:
  • A stopping and starting of the Opto 22 groov EPIC and  SNAP PAC Driver module (through Ignition Edge).
  • Recovery from a communication fault.
  • A download of the strategy.