KB88312
Published: August 22, 2019
Tag browser reports an error on some folders containing 25+ tags
groov View on:
  • GROOV-AT1, GROOV-AT1-SNAP
  • GRV-EPIC-PR1
4.1a to 4.1c
4.1d
In the following circumstances, when you browse for tags on your GRV-EPIC-PR1 (by expanding the device tree in the Gadget Palette), any folders with more than 25 tags will cause an error:
  • Your GRV-EPIC-PR1 device is configured to run the CODESYS Controller.
  • You added the GRV-EPIC-PR1 to your groov View project as an OPC UA Server.
The error message you'll see is similar to the following:
groov cannot browse tags on the OPC server.
Error details:
    Message: ServiceFault: Bad_TooManyOperations (0x80100000) "The request could not be processed because it specified too many operations." Diagnostic Info:
    Status Code: Bad_TooManyOperations (0x80100000) - The request could not be processed because it specified too many operations.
    Exception Name: ServiceException
If possible, reorganize your tag structure and folders so that you do not use more than 25 variables in a single folder.