KB87734
Published:
Storing strategy to flash sometimes fails
This issue affects the following units only if they have hardware revision 04/02/2018 (April 2, 2018) or newer, as viewed in the PAC Manager Status Read page:
- SNAP-PAC-S1, SNAP-PAC-S1-FM
- SNAP-PAC-S2
- SNAP-PAC-R1, SNAP-PAC-R1-FM, SNAP-PAC-R1-B
- SNAP-PAC-R2, SNAP-PAC-R2-FM
To find the date in the PAC Manager Status Read page:
- Start PAC Manager and click Tools > Inspect. PAC Manager opens the Inspect Opto 22 Device window.
- In the Device Name field, type in the IP address or host name of the controller, and then press Enter.
- In the Status Read area, check the following:
- I/O Unit Hardware Revision (Month)
- I/O Unit Hardware Revision (Day)
- I/O Unit Hardware Revision (Year)
9.5g
PAC Firmware R9.5h
When downloading a PAC Control strategy with the option set to store the strategy to flash, sometimes it will fail with a message that says:
Unable to store strategy into flash memory.
A problem occurred while attempting to write to flash memory. A possible cause is the flash memory has become unusable and should be replaced."
This can also occur:
- when you select the Control Engine > Save Strategy to Flash menu item while PAC Control is in Debug mode.
- when you inspect the controller with PAC Terminal and then click on the Store to Flash button.