KB84373
Published: January 9, 2015
groov: Cannot clear NaN error received when using the trend gadget
GROOV-AR1
GROOV-AR1-SNAP
GROOV-SVR-WIN
GROOV-SVR-WIN-SNAP
Problem affects versions: R2.3a and lower
In a trend gadget in groov, if you see an error that states, "An unexpected error has occured. Details: Invalid value received from the server: NaN" you are unable to dismiss the error dialog box.
"NaN" stands for "Not a Number" and means that a floating point value is not valid.
In order for the error message to be cleared, the source of the NaN data must be corrected and you must refresh your browser page.
Sometimes the NaN value will correct itself. If it is associated with a SNAP analog module, it is usually caused by low voltage at the I/O rack that contains the analog module.
Try refreshing the browser page. If the NaN is from a SNAP analog module, check voltage at the I/O rack.