KB83648
Published: June 26, 2014
Move Table to I/O Unit does not set digital output IVALs for 4-channel modules when communication is disabled to I/O unit
Problem affects versions: Firmware R9.3e and lower
Resolution is included beginning in version: Firmware R9.4a
In PAC Control, if you use the Move Table to I/O Unit command on an Ethernet-based I/O unit to which communication is disabled, the IVALs for digital outputs on 4-channel digital modules will be set to "Off" regardless of the table values.
The IVALs of high-density digital points and analog points will be updated correctly, but 4-channel digital output IVALs will be set to "Off."
Use the Turn On or Turn Off commands to set the point states instead of using Move Table to I/O Unit.