KB83610
Published: June 26, 2014
Communication to mistic I/O units erroneously disabled by error in PAC Control
Problem affects versions: Firmware R9.3e and lower
Problem is fixed in version: Firmware R9.4a
This problem applies only to mistic I/O units connected to SNAP PAC controllers running PAC Control.
If an I/O command results in an error, communication to the mistic I/O unit may be disabled, even if the error is not related to communications.
As one example, if you're using the TPO feature on a digital output, you must set the TPO Period before setting the TPO Percent, or else an error will occur. If you re-enable communication to the I/O unit that has the digital TPO output point, and then set the TPO Percent before setting the TPO Period, communication to that I/O unit will become disabled.
Here's how you can work around it:
Use a "gateway" variable around any usage of the Set TPO percent command.
When your I/O enabler chart detects that the I/O unit has been disabled, it must:
  • Set the gateway variable to a value that lets other charts know not to set the TPO percentage
  • Enable the I/O unit
  • Set the TPO Period
  • Set the gateway variable to a value that lets other charts know that it's ok to use the command Set TPO Percent