SNAP-ODC5R5FM
Hover over image to zoom in

Availability: Obsolete
OBSOLETE SNAP 4-Ch Low-voltage Mechanical Relay Digital (Discrete) Output Module, Normally Closed

Production Specification

*** NOTE: This part is OBSOLETE and no longer available. ***
Contact Opto 22 Pre-Sales engineers for more information or see Form 2411, Obsolete SNAP 4-Channel Digital I/O Technical Note.

The SNAP-ODC5R5FM is a digital output module that uses low-voltage mechanical relays and does not provide optical isolation. Current rating depends on the voltage the module is used with. This module is normally closed. It includes a connector clamp to prevent sparks.

Typical applications for these modules include analog signal and communication line multiplexing. Because of their low 10 VA rating, these modules are not recommended for inductive or capacitive loads (even very small loads) because the inrush current is likely to exceed the 10 VA rating.

IMPORTANT: Applications using 120 VAC are typically NOT suited to this module. If you are considering using this module for any application other than low-voltage purely resistive loads, see the detailed notes and rating curve in the data sheet, and call Pre-sales Engineering for specific guidance.

For many applications a better choice is the SNAP-OMR6-C module, which can handle a full 6 A at 0-250 VAC or 0-30 VDC.
Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

For easier, faster wiring, see SNAP TEX cables and breakout boards.

Build your system in the SNAP I/O Configurator.

 

SNAP-ODC5RFM
[Obsolete]

SNAP-ODC5R5FM
[Obsolete]

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

Field Side Ratings (each channel)

Line Voltage - Range

0–100 VDC
0–130 VAC*

0–100 VDC
0–130 VAC*

Line Voltage - Nominal

--

--

Current Rating

0.5 amps switching*

0.5 amps switching*

Surge Current

0.5 amps*

0.5 amps*

Minimum Load

0 mA

0 mA

Output Voltage Drop

0 volts

0 volts

Off-state Leakage

0 mA

0 mA

Peak Blocking Voltage

100 VDC / 130 VAC

100 VDC / 130 VAC

Fuse
(Common to all Channels)

Has four isolated channels. User must provide own fusing.

Has four isolated channels. User must provide own fusing.

Logic Side Ratings

Pickup Voltage

4 V @ 5.5 mA

4 V @ 5.5 mA

Dropout Voltage

1 VDC

1 VDC

Control Resistance

220 ohms

220 ohms

Logic Supply Voltage

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

Logic Supply Current

50 mA maximum

50 mA maximum

Module Ratings

Number of Channels Per Module

4

4

Turn-on Time

500 usec

500 usec

Turn-off Time

500 usec

500 usec

Isolation (Field Side to Logic Side)

1,500 volts (transient)

1,500 volts (transient)

Mechanical Life

200,000,000 cycles

200,000,000 cycles

Temperature

-20 to 70 °C, operating
-30 to 85 °C, storage

-20 to 70 °C, operating
-30 to 85 °C, storage

Agency Approvals

CE, RoHS, DFARS; UKCA

CE, RoHS, DFARS; UKCA

Warranty

30 months or mechanical life, whichever comes first

30 months or mechanical life, whichever comes first

* The current of the dry contact module must not exceed 10 VA power rating under steady state or momentary in-rush conditions. For voltages at or below 20 volts, the current limit is 0.5 amps. For voltages above 20 volts, the maximum allowable current is determined by the following equation:
Current Maximum = 10 VA / Voltage. Rating curve is in the data sheet.

Obsolete SNAP 4-Channel Digital I/O Technical Note

This technical note contains information you may need about OBSOLETE SNAP 4-Channel Digital I/O modules you’re still using. Included are part numbers, descriptions, specifications, wiring diagrams, and dimensional drawings. These parts have been removed from data sheets because we no longer sell them. 

This document includes information on the following obsolete types of SNAP 4-channel digital I/O modules:


 

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

No downloads are available for this product.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.

Video: Securing SNAP Module

A quick overview on securing a SNAP Module to a SNAP rack.

Video: Removing a SNAP Module

A quick overview on removing a SNAP module.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.