SNAP-IDC5DFM
Hover over image to zoom in

SNAP-IDC5DFM

$71.50 (USA and Canada only)

Availability: In stock
OBSOLETE SNAP 4-Ch 2.5-28 VDC Digital Input Module, Factory Mutual approved

Production Specification

** NOTE: This part is OBSOLETE and no longer available when current stock is depleted. ***
Please contact Opto 22 Pre-Sales engineers for more information.

The SNAP-IDC5DFM provides four channels of 2.5-28 VDC digital input. Each channel senses the on/off status for DC voltages from sources such as proximity switches, push buttons, or auxiliary contacts. It has removable top-mounted connectors for easy access to field wiring, as well as channel-specific LEDs for convenient troubleshooting.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

For easier, faster wiring, see SNAP TEX cables and breakout boards.

Build your system in the SNAP I/O Configurator.

 

SNAP-IAC5FM
[Obsolete]

SNAP-IAC5AFM
​[Obsolete]

SNAP-IDC5FM
​[Obsolete]

SNAP-IDC5DFM
​[Obsolete]

Wire size

22 to 14 AWG

22 to 14 AWG

22 to 14 AWG

22 to 14 AWG

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

Field Side Ratings (each channel)

Nominal Input Voltage

120 VAC/VDC

240 VAC/ VDC

24 VAC/VDC

5 VDC

Channel-to-channel
isolation

300 VAC
(1,500 V transient)

300 VAC
(1,500 V transient)

300 VAC
(1,500 V transient)

300 VAC
(1,500 V transient)

Input Voltage Range

90–140 VAC/VDC

180–280 VAC/VDC

10–32 VAC/VDC

2.5–28 VDC

Turn-on Voltage

90 VAC/VDC

180 VAC/VDC

10 VAC/VDC

2.5 VDC

Turn-off Voltage

35 VAC/VDC

35 VAC/VDC

3 VAC/VDC

1 VDC

Input Resistance

169 K ohms (nominal)

305 K ohms (nominal)

15 K ohms (nominal)

3 K ohms (nominal)

Logic Side Ratings

Logic Output Voltage

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 400 mA sourcing

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 400 mA sourcing

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 0.4 mA sourcing

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 0.4 mA sourcing

Logic Supply Voltage*

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

Logic Supply Current

50 mA maximum

50 mA maximum

50 mA maximum

50 mA maximum

Negative True Logic
Output Drive

TTL 74 Series=1 UL
TTL 74LS Series=5 UL

TTL 74 Series=1 UL
TTL 74LS Series=5 UL

TTL 74 Series=1 UL
TTL 74LS Series=5 UL

TTL 74 Series=1 UL
TTL 74LS Series=5 UL

Module Ratings

Number of Channels
Per Module

4

4

4

4

Turn-on Time

30 msec

30 msec

5 msec

1 msec

Turn-off Time

30 msec

30 msec

15 msec

1 msec

Optical Isolation
(Field Side to
Logic Side)

4,000 volts (transient)

4,000 volts (transient)

4,000 volts (transient)

4,000 volts (transient)

Temperature

-20 to 70 °C, operating
-40 to 85 °C, storage

-20 to 70 °C, operating
-40 to 85 °C, storage

-20 to 70 °C, operating
-40 to 85 °C, storage

-20 to 70 °C, operating
-40 to 85 °C, storage

Agency Approvals

CE, FM, RoHS, DFARS; UKCA

CE, FM, RoHS, DFARS; UKCA

CE, FM, RoHS, DFARS; UKCA

CE, ATEX, FM, RoHS, DFARS; UKCA

Warranty

Lifetime

Lifetime

Lifetime

Lifetime

*When used with an I/O processor (brain or on-the-rack controller), the processor requires 5.0 to 5.2 VDC.

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

SNAP Digital Input Modules Data Sheet

SNAP digital input modules are designed to work with SNAP PAC racks and can sense either AC or DC signals.

All SNAP digital input modules are compatible with SNAP PAC brains and R-series controllers, including Wired+Wireless models.

Most digital input modules are also compatible with SNAP D-series or legacy M-series and B-series racks and with the brains that mount on them.

This data sheet applies to:

UKCA Declaration of Conformity (ATEX, EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with the rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (ATEX, EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

CE Declaration of Conformity: ATEX

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with the mentioned European, international and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

CSA Approval Document

This document lists all Opto 22 part numbers that have the Canadian Standards Association (CSA) approval.

CAD 3D Drawing: SNAP-IDC5D Digital Input Module

This CAD file contains a 3-dimensional drawing of the SNAP-IDC5D digital input module, which provides four channels of 2.5-28 VDC digital input. This drawing also applies to the SNAP-IDC5DFM, which is Factory Mutual approved.

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: Securing SNAP Module

A quick overview on securing a SNAP Module to a SNAP rack.

Video: Removing a SNAP Module

A quick overview on removing a SNAP module.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.