SNAP 4-Ch 2.5-28 VDC Digital (Discrete) Input Module

Production Specification

The SNAP-IDC5D provides four channels of 2.5-28 VDC digital input. Each channel senses the on/off status for DC voltages from sources such as proximity switches, push buttons, or auxiliary contacts. The module has removable top-mounted connectors for easy access to field wiring, as well as channel-specific LEDs for convenient troubleshooting.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

For easier, faster wiring, see SNAP TEX cables and breakout boards.

Build your system in the SNAP I/O Configurator.

 

SNAP-IDC5

SNAP-IDC5D

SNAP-IDC5G

SNAP-IDC5-HT

Key Feature

--

--

--

Leakage-tolerant

Wire size

22 to 14 AWG

22 to 14 AWG

22 to 14 AWG

22 to 14 AWG

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

5.22 in-lb (0.59 N-m)

Field Side Ratings (each channel)

Nominal Input Voltage

24 VAC/VDC

5 VDC

48 VAC/VDC

24 VAC/VDC

Channel-to-channel isola­tion

300 VAC
(1,500 V transient)

300 VAC
(1,500 V transient)

300 VAC
(1,500 V transient)

300 VAC
(1,500 V transient)

Input Voltage Range

10–32 VAC/VDC

2.5–28 VDC

35–75 VAC/VDC

15–32 VAC/VDC

Turn-on Voltage

10 VAC/VDC

2.5 VDC

35 VAC/VDC

15 VAC/VDC

Turn-off Voltage

3 VAC/VDC

1 VDC

7 VAC/VDC

8 VAC/VDC

Input Resistance

15 K ohms (nominal)

3 K ohms (nominal)

64 K ohms (nominal)

3 K ohms (nominal)

Logic Side Ratings

Logic Output Voltage

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 0.4 mA sourcing

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 0.4 mA sourcing

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 0.4 mA sourcing

<.5 V max. (on)
@ 2 mA sinking
2.7 V min. (off)
@ 0.4 mA sourcing

Logic Supply Voltage***

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

5 VDC ± 0.25 VDC

Logic Supply Current

50 mA maximum

50 mA maximum

50 mA maximum

50 mA maximum

Negative True Logic Out­put Drive

TTL 74 Series = 1 UL
TTL 74LS Series = 5 UL

TTL 74 Series = 1 UL
TTL 74LS Series = 5 UL

TTL 74 Series = 1 UL
TTL 74LS Series = 5 UL

TTL 74 Series = 1 UL
TTL 74LS Series = 5 UL

Module Ratings

 

 

Number of Channels Per Module

4

4

4

4

Turn-on Time

5 msec

1 msec

5 msec

20 msec

Turn-off Time

15 msec

1 msec

15 msec

25 msec

Optical Isolation
(Field Side to Logic Side)

4,000 volts (transient)

4,000 volts (transient)

4,000 volts (transient)

4,000 volts (transient)

Temperature

-20 °C to 70 °C, operating
-40 °C to 85 °C, storage

-20 °C to 70 °C, operating
-40 °C to 85 °C, storage

-20 °C to 70 °C, operating
-40 °C to 85 °C, storage

-20 °C to 70 °C, operating
-40 °C to 85 °C, storage

Agency Approvals

UL, CE, CSA, RoHS, DFARS, NEBS; UKCA

UL, CE, CSA, RoHS, DFARS; UKCA

UL, CE, RoHS, DFARS; UKCA

CE, RoHS, DFARS; UKCA

Warranty

Lifetime

Lifetime

Lifetime

Lifetime

* At 20kHz, 5Vp-p square wave input, 50% duty cycle.
** At 20kHz, 28Vp-p square wave input, 50% duty cycle.
*** When used with an I/O processor (brain or on-the-rack controller), the processor requires 5.0 to 5.2 VDC.

SNAP Digital Input Modules Data Sheet

SNAP digital input modules are designed to work with SNAP PAC racks and can sense either AC or DC signals.

All SNAP digital input modules are compatible with SNAP PAC brains and R-series controllers, including Wired+Wireless models.

Most digital input modules are also compatible with SNAP D-series or legacy M-series and B-series racks and with the brains that mount on them.

This data sheet applies to:

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

Digital I/O for Raspberry Pi Selection Guide

Now you can safely and reliably sense and switch industrial-level electrical loads with your Raspberry Pi® and Opto 22 industrially hardened digital I/O.

This Selection Guide describes compatible I/O racks and modules, power supplies, and accessories that work with the Raspberry Pi and the Digital I/O Carrier Board for the Pi (OPTO-P1-40P). Specifications, dimensional drawings, and wiring diagrams for racks and I/O modules are included.

For code samples and steps to get started, also see developer.opto22.com.

UKCA Declaration of Conformity (ATEX, EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity  for the products listed herein, in accordance with ATEX, EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (ATEX, EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

CSA Approval Document

This document lists all Opto 22 part numbers that have the Canadian Standards Association (CSA) approval.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

CAD 3D Drawing: SNAP-IDC5D Digital Input Module

This CAD file contains a 3-dimensional drawing of the SNAP-IDC5D digital input module, which provides four channels of 2.5-28 VDC digital input. 

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.

Video: Securing SNAP Module

A quick overview on securing a SNAP Module to a SNAP rack.

Video: Removing a SNAP Module

A quick overview on removing a SNAP module.

Video: Automation 101: Wire a Proximity Sensor

Learn how you can wire a proximity sensors to gather machine data without ever touching equipment and without interfering in your process.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.