OBSOLETE Three-phase Power Monitoring Module, 85-300 V RMS and 0-0.333 VAC CT Inputs for Each Phase

Production Specification

*** NOTE: This part is obsolete and no longer available. ***

SNAP-AIPM-3V analog input module helps you measure and control power usage in your facility. The SNAP-AIPM-3V module simultaneously measures volts AC RMS and amps AC RMS for each of the three phases, using current transformers (CTs) with a 0.333 VAC secondary. These CTs are safer and less expensive than CTs that output current.

Using the data from the voltage and current inputs, the module then calculates true power and volt-amps for each phase and, in addition, calculates true power sums for all three phases.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

When these modules are used as part of a SNAP PAC System running a PAC Control strategy, the strategy logic can automatically perform the calculations and respond to problems.

Processor compatibility: SNAP-AIPM-3V modules work with SNAP PAC brains and R-series controllers. They require brain firmware version 9.1b or newer and PAC Project 9.1a or newer.

See compatible split-core CTs.

Other power monitoring input modules:
  • SNAP-AIPM monitors single-phase power.
  • SNAP-AIPM-3 monitors three-phase power using CTs with a 1-5 Amp secondary.
NOTE: SNAP-AIPM-3V modules manufactured before April 2011 had a different voltage input range (0-250 VAC). Specs were changed to allow connection to electrical systems and equipment at higher voltages (for example, lighting systems at 277 volts). Before wiring or scaling any SNAP-AIPM-3V, check the input range printed on the module. Scaling examples are in the data sheet. Older modules can be exchanged for newer ones; contact Product Support for information or answers to questions.

Build your system in the SNAP I/O Configurator.

 

SNAP-AIPM-3

SNAP-AIPM-3V [OBSOLETE]

Voltage Inputs (each voltage channel)

Recommended Input Range
Scaled Input Range


85 to 300 VAC RMS*
0 to 300 VAC RMS


85 to 300 VAC RMS*
0 to 300 VAC RMS

Input Over Range

To 330 volts

To 330 volts

Resolution

12 mV

12 mV

Accuracy (47 to 63 Hz)

(When used within recommended range)
± 0.2 V plus ± 0.2% reading (at full scale = ± 0.7 V or 0.28%)

(When used within recommended range)
±0.2 V plus ±0.2% reading (at full scale = ±0.2 V + ±0.8 V = ±1.0 V)

RMS Integration Time/ Data Freshness

1000 ms (synchronous with current measurement)

1000 ms (synchronous with current measurement)

Input Filtering

Time constant = 70 µs (analog front end)
(-0.2 dB at 660 Hz; -3 dB at 1.89 kHz) nominal

Time constant = 70 µs (analog front end)
(-0.2 dB at 660 Hz; -3 dB at 1.89 kHz) nominal

Input Resistance - Single Ended

1 Megohm
NOTE: Because both channels share the same reference terminal, polarity must be observed when connecting the current channel.

1 Megohm
NOTE: Because both channels share the same reference terminal, polarity must be observed when connecting the current channel.

Maximum Input

330 V non-operating

330 V non-operating

Current Inputs (each current channel)

Input Range

0 to 5 AC amps RMS*

0 to 0.333 VAC current transformer input

Input Over Range

To 5.5 amps (Reading is not reliable over 5.5 A)

To 0.366 VAC

Input Overload

15 A continuous, non-operating

5 VAC continuous, non-operating

Resolution

200 µA

13.3 µV AC

Accuracy (47 to 63 Hz)

± 4 mA plus ± 0.2% reading (at full scale = ± 28 mA or 0.28%)

± 266 microvolts plus 0.2% of reading (at full scale = 266 µV + 667 µV = 933 µV = 0.28%)

RMS Integration Time/ Data Freshness

1000 ms (synchronous with voltage measurement)

1000 ms (synchronous with voltage measurement)

Input Filtering

Time constant = 105 µs (analog front end)
(-0.2 dB at 660 Hz; -3 dB at 1.89 kHz) nominal

Time constant = 105 µs (analog front end)
(-0.2 dB at 660 Hz; -3 dB at 1.89 kHz) nominal

Input Resistance - Single Ended

0.005 Ohm
NOTE: Because both channels share the same reference terminal, polarity must be observed when connecting the voltage channel.

500 K Ohms
NOTE: Because both channels share the same reference terminal, polarity must be observed when connecting the voltage channel.

Maximum Input

15 A continuous, non-operating

5 VAC continuous, non-operating

Calculated Channels

True Power and Volt-Amps Range

True power: 1500.0 Watts. Volt-amps: 1500.0 volt-amps
(inputs = 300 volts and 5 amps)

True power and volt-amps are calculated from 300 volts and the full-scale current input of your 0.333 VAC output CT.

Over Range

1650 Watts true power or 16,500 counts volt-amps

Depends on CT selection

Accuracy:

 

 

True Power
Volt-Amps

± 0.6% reading (at full scale = ± 15 Watts)
± 0.6% reading (at full scale = ± 15 VA)

± 0.6% reading
± 0.6% reading

Resolution

100 mW with default scaling

Depends on CT selection

AC Common Mode Rejection

> -120 dB at 60 Hz

> -120 dB at 60 Hz

Maximum Operating Common Mode Voltage

300 VAC

300 VAC

Calculated Outputs

True Power

0-1500 W (from synchronous measurement of volts and amps)

W (from synchronous measurement of volts and amps)**

Volt Amps

0-1500 VA (VRMS x ARMS)

VA (VRMS x ARMS)**

1-second Energy Sum

0-4500 joules (true power sum ABC, signed)

Joules (true power sum ABC, signed)**

1-second abs Energy Sum

0-4500 joules (true power sum of absolute value of each A, B, and C, always positive)

Joules (true power sum of absolute value of each A, B, and C, always positive)**

General Specifications

Power Requirements

5.0 VDC ± 0.15 VDC at 100 mA

5.0 VDC ± 0.15 VDC at 100 mA

Ambient Temperature:

Operating
Storage

 

-20 to 70 °C
-40 to 85 °C

 

-20 to 70 °C
-40 to 85 °C

Humidity

5-95%, non-condensing

5-95%, non-condensing

Agency Approvals

CE, RoHS, DFARS

CE, RoHS, DFARS

Warranty

Lifetime

Lifetime

*Inputs on older modules were 0-250 V and for SNAP-AIPM-3, 0-10 A. Before wiring or scaling, check printed information on the module to make sure you are using the correct voltage and current. Contact Opto 22 Product Support with any questions.

**Values depend on CT selection.

SNAP Power Monitoring Modules Data Sheet

"*** NOTE: SNAP-AIPM and SNAP-AIPM-3V are obsolete and no longer available. SNAP-AIPM-3 is obsolete when current stock is depleted.  *** 
Please contact Opto 22 Pre-Sales engineers for more information.

This data sheet describes the SNAP-AIPM, SNAP-AIPM-3, and SNAP-AIPM-3V analog input modules. These modules monitor AC voltage and current through a SNAP PAC rack-mounted controller or SNAP PAC brain.

The SNAP-AIPM monitors single-phase AC. The SNAP-AIPM-3 and SNAP-AIPM-3V monitor three-phase AC.

The SNAP-AIPM not only measures volts and amps simultaneously, but also calculates true power and volt-amps. From these values, you can easily calculate power factor. The SNAP-AIPM-3 and SNAP-AIPM-3V measure volts and amps and calculate true power and volt-amps for each of the three phases, and in addition calculate true power sums for all three.

Energy Monitoring for Profit: Introducing Demand Response

This white paper introduces the concept of demand response (DR) in energy management. DR offers an opportunity for industrial and commercial businesses to not just reduce energy costs, but also earn a revenue stream from their use of electrical energy.

The paper briefly discusses how electrical energy is produced and distributed in the United States and then describes four practical steps automation professionals can begin now to take advantage of DR programs in their area.

Automatización y La Red Inteligente (Smart Grid): Gestión de Energía

Automatización y La Red Inteligente (Smart Grid): Gestión de Energía is a white paper in Spanish.

To read this white paper in English, see Form 1914, Automation and the Smart Grid: Energy Management Today.

Automação e a Rede Inteligente (Smart Grid): Gestão de Energia

Automação e a Rede Inteligente (Smart Grid): Gestão de Energia is a white paper in Portuguese.

To read this white paper in English, see Form 1914, Automation and the Smart Grid: Energy Management Today.

Automation and the Smart Grid: Energy Management Today

This white paper looks at the way electricity is produced in the United States today and the vision for a "Smart Grid" in the future.

The paper also discusses specific ways that small and medium-sized industrial and commercial businesses can manage electrical usage and costs today, without waiting for Smart Grid technology.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

Pulse Energy Quick Start

Pulse Energy is an online service you can use to view data about your electrical energy usage. Support for Pulse Energy is integrated into the OptoEMU Sensor™; however, if you are not using the Sensor but acquiring energy data using the SNAP PAC System, you can still see that data through Pulse Energy.

This sample chart shows you how to move data from PAC Control into Pulse. Import the included chart into your PAC Control strategy to make integration with a Pulse Energy account easier. The included technical note, form 1992, shows you how to configure a Pulse Energy account and use the chart to visualize your monitored energy values.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.