SNAP-AIMV-4
Hover over image to zoom in

SNAP-AIMV-4

$408.00 (USA and Canada only)

Availability: Call for Availability
SNAP 4-Ch -150 to +150 mV Analog Input Module

Production Specification

The SNAP-AIMV-4 provides four channels of analog-to-digital conversion. Each channel can be configured for -150 mV DC to +150 mV DC or -75 mV DC to +75 mV DC. Although the four channels are not isolated from each other, the module is transformer isolated and optically isolated from other modules and devices.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

Compatibility: This module can be used with SNAP PAC brains and R-series controllers. It can also be used with legacy Ethernet-based brains.

Build your system in the SNAP I/O Configurator.

Input Range

From -150 mV to +150 mV
From -75 mV to +75m V

Over-Range Limits

From -165 to +165 mV
(+/-150 mV range)
From -82.5 to +82.5 mV
(+/-75 mV range)

Resolution

6 microvolts (-150 mV to +150 mV)
3 microvolts (-75 mV to +75 mV)

Input Filtering

-3 dB @ 7 Hz

Input Response Time (% of span/delta V/delta time)

63.2%/95 mV/23 ms

Data Freshness (Max)

335 ms (+/- 150 mV)
668 ms (+/- 75 mV)

DC Common Mode Rejection

>-120 dB

AC Common Mode
Rejection

>-120 dB @ 60 Hz

Maximum Survivable Input

±15 volts

Maximum Operating
Common Mode Voltage

250 V

Accuracy at Full Scale

0.06% (90 microvolts) @ 150 mV
0.1% (75 microvolts) @ 75 mV

Drift: Gain Temperature Coefficient

3 microvolts / °C

Drift: Offset Temperature Coefficient

2 microvolts / °C

Isolation

1500 V

Power Requirements

5 VDC (±0.15 ) @ 170 mA

Input Resistance - Single Ended

100 Megohms (each channel)

Operating Temperature

-20 °C to 70 °C

Storage Temperature

-40 °C to 85 °C

Humidity

5-95%, non-condensing

Wire size

22 to 14 AWG

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

Agency Approvals

UL, CE, RoHS, DFARS; UKCA

Warranty

Lifetime

SNAP Analog Input Modules Data Sheet

SNAP I/O analog input modules are part of Opto 22's SNAP PAC System. This document includes descriptions, specifications, and wiring and dimensional diagrams for the following analog input modules:

For analog modules with channel-to-channel isolation, see Form 1182, the SNAP Isolated Analog Input Modules Data Sheet.

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

SNAP I/O Modules Firmware Release Notes

This document lists the latest updates to the firmware for SNAP I/O modules. It includes information on new features, enhancements, and bug fixes.

List of SNAP I/O module firmware download pages

NOTE: This document was formerly called a readme. The name was changed to more accurately describe its content.

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: EMC

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

SNAP-AIMV-4 Module Firmware

This download contains current firmware for the SNAP-AIMV-4 four-channel analog input module for analog-to-digital conversion.

For a list of bug fixes and enhancements included in this firmware, see the SNAP I/O Modules Firmware Release Notes.

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.