SNAP 2-Ch Isolated -1 mA to +1 mA Analog Current Input Module

Production Specification

The SNAP-AIMA2-i module provides two isolated channels with an input range of -1 mA to +1 mA. This module does not supply loop excitation current.

Part of the SNAP PAC System, the module mounts on a SNAP PAC rack with a SNAP PAC brain or rack-mounted controller. Analog, digital, and serial I/O modules can all be on the same rack. Such an I/O unit is also well suited for PC-based control or for use as intelligent remote I/O for an Allen-Bradley Logix PLC system, such as ControlLogix, MicroLogix, or CompactLogix.

Build your system in the SNAP I/O Configurator.

Input Range

-1 mA to +1 mA

Maximum Over Range

±10% (=± 27500 counts)

Resolution

0.04 µA

Input Response Time
(% of span/delta I/delta time)

99.9 %/19.9 µA/10 ms

Data Freshness

11 ms

DC Common Mode Rejection

>-120 dB

AC Common Mode Rejection

>-120 dB @ 60 Hz

Maximum Survivable Input

11 mA or 28 VDC

Maximum Operating Common Mode Voltage

250 V

Accuracy

0.05% (0.05 µA)

DRIFT: Gain Temperature Coefficient

30 PPM/ °C

DRIFT: Offset Temperature Coefficient

15 PPM/ °C

Isolation: Optical

4000 V

Isolation: Transformer

1500 V

Isolation: Channel to Channel

250 V continuous
(1500 V transient)

Power Requirements

5 VDC (±0.15 V) at 200 mA

Input Resistance

5 K ohms (each channel)

Ambient Temperature:
  Operating
  Storage

 

-20 °C to 70 °C
-40 °C to 85 °C

Humidity

5-95%, non-condensing

Torque, hold-down screws

Not to exceed 1 in-lb (0.11 N-m)

Torque, connector screws

5.22 in-lb (0.59 N-m)

Wire size range

22 to 14 AWG

Agency Approvals

CE, RoHS, DFARS

Warranty

Lifetime

SNAP Isolated Analog Input Modules Data Sheet

The isolated analog input modules described in this document are part of Opto 22's SNAP PAC System. They provide optical isolation, transformer isolation, and channel-to-channel isolation. This data sheet covers the following part numbers:

SNAP PAC System Product Guide

This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.

SNAP I/O Modules Firmware Release Notes

This document lists the latest updates to the firmware for SNAP I/O modules. It includes information on new features, enhancements, and bug fixes.

List of SNAP I/O module firmware download pages

NOTE: This document was formerly called a readme. The name was changed to more accurately describe its content.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

SNAP-AIMA2-i Module Firmware

This download contains current firmware for the SNAP-AIMA2-i two-channel, isolated -1 mA to +1 mA analog current input module.

For a list of bug fixes and enhancements included in this firmware, see the SNAP I/O Modules Firmware Release Notes.

CAD Drawing: SNAP I/O Module

This CAD file includes drawings that apply to most SNAP analog and digital I/O modules.

Video: SNAP PAC System Overview

This overview describes the four integrated components of the SNAP PAC system: software, controllers, brains and I/O. This hardware and software system is designed for industrial control, remote monitoring and data acquisition.

Video: Securing SNAP Module

A quick overview on securing a SNAP Module to a SNAP rack.

Video: Removing a SNAP Module

A quick overview on removing a SNAP module.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.