$393.00 (USA and Canada only)
Input Range
From -50 mV to +50 mVDC From -25 mV to +25 mVDC
Maximum Over Range
± 10% (= ± 27500 counts)
Resolution
2 µV from -50 mV to +50 mV 1 µV from -25 mV to +25 mV
Cold Junction Temperature Compensation
Automatic when used with SNAP brains
Input Filtering
-3 dB @ 2.4 Hz
Input Response Time (% of span/delta V/delta time)
63.2%/31.5 mV/66 ms
Data Freshness
65 ms for +/- 50 mV 130 ms for +/- 25 mV 130 ms for B-, R-, S-, and T-type thermocouples 65 ms for C-, D-, G-, and N-type thermocouples
DC Common Mode Rejection
>-120 dB
AC Common Mode Rejection
>-120 dB @ 60 Hz
Maximum Survivable Input
±15 volts
250 V
Accuracy
0.1% (50 µV) @ 50 mV (full scale) 0.2% (50 µV) @ 25 mV (full scale)
Drift: Gain Temperature Coefficient
5 µV / °C
Drift: Offset Temperature Coefficient
2 µV / °C
Thermocouple Accuracy [°C] From factory After user gain and offset commands
B, R, S C, D, G T, N ±5 ±4 ±3 ±3 ±2 ±2
Isolation: Optical
4000 V
Isolation: Transformer
1500 V
Isolation: Channel to Channel
250 V continuous (1500 V transient)
Power Requirements
5 VDC (±0.15 ) @ 200 mA
Input Resistance
100 megohms (each channel)
Ambient Temperature: Operating Storage
-20 °C to 70 °C -40 °C to 85 °C
Humidity
5-95%, non-condensing
Torque, hold-down screws
Torque, connector screws
3 in-lb (0.34 N-m)
Wire size range
22 to 14 AWG
CE, RoHS, DFARS; UKCA
Lifetime
This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.
The isolated analog input modules described in this document are part of Opto 22's SNAP PAC System. They provide optical isolation, transformer isolation, and channel-to-channel isolation. This data sheet covers the following part numbers:
This white paper describes various temperature sensors such as RTDs, thermocouples, ICTDs, thermistors, and infrared sensors, and the Opto 22 solutions for using them.
This primer describes various temperature sensors such as RTDs, thermocouples, ICTDs, thermistors, and infrared sensors, and the Opto 22 solutions for using them.
This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.
A quick overview on I/O Solutions for temperature monitoring.
$289.00
$630.00