Analog voltage input, 24 channels, 8 configurable input ranges from ±160 V to ±1.25 VDC, no channel-to-channel isolation

Production Specification

Part of the groov EPIC® system, the GRV-IV-24 analog module can be configured for any one of the following eight input ranges on each of its 24 input channels:
  • ±160.0 VDC
  • ±80.0 VDC
  • ±40.0 VDC
  • ±20.0 VDC
  • ±10.0 VDC
  • ±5.0 VDC
  • ±2.5 VDC
  • ±1.25 VDC
Note that all channels share a common reference terminal. The module cover includes an LED that indicates status and a touch-sensitive pad. Touch the pad and the groov EPIC processor displays information about the module, including specifications and a wiring diagram.

The GRV-IV-24 module mounts on a groov EPIC chassis together with a GRV-EPIC-PR1 processor and other analog, discrete, and serial groov I/O modules.

All groov I/O modules are UL/cUL listed and compliant with the ATEX, Low Voltage, and EMC CE and UKCA directives. Each module is factory tested twice before shipment and most modules are guaranteed for life.

Opto Products, like GRV-IV-24, are ideal for OEMs and machine designers, process control, machine monitoring, power and energy monitoring, predictive maintenance, remote installations like water-wastewater and oil & gas, SCADA, and industrial internet of things applications.
Feature
 GRV-IV-24   
 GRV-IVI-12  
 GRV-IVIRMS-10
Number of Channels
24
12
10
Channel-to-Channel Isolation
 
⬤
⬤
Analog Totalizing
⬤
⬤
⬤
Average Filter Weight
⬤
⬤
⬤
Minimum/Maximum Values
⬤
⬤
⬤
Offset and Gain
⬤
⬤
⬤
Quality Indication
⬤
⬤
⬤
Scaling
⬤
⬤
⬤
Simple Moving Average
⬤
⬤
⬤
 

Specification

GRV-IV-24

GRV-IVI-12

GRV-IVIRMS-10

Input Ranges

±160.0 VDC ±80.0 VDC
±40.0 VDC ±20.0 VDC
±10.0 VDC ±5.0 VDC
±2.5 VDC ±1.25 VDC

±160.0 VDC ±80.0 VDC
±40.0 VDC ±20.0 VDC
±10.0 VDC ±5.0 VDC
±2.5 VDC ±1.25 VDC

300.0 V rmsAC/DC 150.0 V rms AC/DC
60.0 V rms AC/DC 30.0 V rms AC/DC
20.0 V rms AC/DC 10.0 V rms AC/DC
5.0 V rms AC/DC 1.0 V rms AC/DC
0.5 V rms AC/DC

Over-range Limits

±176.0 VDC ±88.0 VDC
±44.0 VDC ±22.0 VDC
±11.0 VDC ±5.5 VDC
±2.75 VDC ±1.375 VDC

±176.0 VDC ±88.0 VDC
±44.0 VDC ±22.0 VDC
±11.0 VDC ±5.5 VDC
±2.75 VDC ±1.375 VDC

333.0 V rms AC/DC 165.0 V rms AC/DC
66.0 V rms AC/DC 33.0 V rms AC/DC
22.0 V rms AC/DC 11.0 V rms AC/DC
5.5 V rms AC/DC 1.1 V rms AC/DC
0.55 V rms AC/DC

Resolution

Range / 1,048,576 (20-bits)

Range / 1,048,576 (20-bits)

Range / 1,048,576 (20-bits)

Accuracy ±0.1% of Full Scale

±160 mV ±80 mV ±40 mV
±20 mV ±10 mV ±5 mV
±2.5 mV ±1.25 mV

±160 mV ±80 mV ±40 mV
±20 mV ±10 mV ±5 mV
±2.5 mV ±1.25 mV

N/A

Accuracy @ 50-60 Hz

N/A

N/A

±200 mV and ±0.2% of reading

Accuracy @ 60-400 Hz

N/A

N/A

±200 mV and ±0.3% of reading

Input Impedance Nominal

9.7 megohms

9.7 megohms

9.5 megohms

Input Filter

-3 dB at 46 HZ

-3 dB at 46 HZ

N/A

DC Reversal

N/A

N/A

1% of Range

Analog Data Filtering

-3 dB @ 2.4 Hz
-25 dB @ 60 Hz

-3 dB @ 46 Hz
-5 dB @ 60 Hz

N/A

Software Data Filtering:

  • Simple Moving Average (SMA)

  • Weighted Average

 

  • 1 to 32 readings

  • 1 to 4096

 

  • 1 to 32 readings

  • 1 to 4096

 

  • 1 to 32 readings

  • 1 to 4096

Data Refresh Time

450 ms

15.5 ms

50 ms

Step Input Response Time

450 ms x SMA value
(14.4 s @ 32 SMA, Default SMA = 4)

16.5 ms x SMA value
(0.53 s @ 32 SMA, Default SMA = 4)

  • 250 ms x SMA value (1 s @ SMA = 4)

  • 100 to 0%: 1,100 ms x SMA value (4.4 s @ SMA = 4)

Common Mode Rejection

> -120 dB

> -120 dB

> -120 dB

Max. Survivable Input

300 V

300 V

330 V

Max. Operating Common
Mode Voltage

250 V

250 V

300 V

Quality Indications

out of range

out of range

out of range

Isolation (field-to-logic)

300 V working,
1500 V transient (1 minute)

300 V working,
1500 V transient (1 minute)

300 V working,
1500 V transient (1 minute)

Isolation (channel-to-channel)

300 V between
channel group 0-11 & group 12-23

300 V working,
1500 V transient (1 minute)

300V working,
1500 V transient

Number of Channels

24

12

10

Chassis Power Consumption

1.0 W

2.2 W

1.5 W

Minimum groov EPIC
Firmware Version

1.0.0

1.4.2

1.5.0

Minimum PAC Project Version

10.0000

10.2003

10.2005

Minimum Library Package for CODESYS Version

1.0.0.0

1.0.2.0

1.0.3.0

Wire Size

28-14 AWG

28-14 AWG

28-14 AWG

Wire Strip Length

0.315–0.354 inches (8–9 mm)

0.315–0.354 inches (8–9 mm)

0.315–0.354 inches (8–9 mm)

Torque, connector screw

2.5 in-lb (0.28 N-m)

2.5 in-lb (0.28 N-m)

2.5 in-lb (0.28 N-m)

Torque, hold-down screw

3.5 in-lb (0.4 N-m)

3.5 in-lb (0.4 N-m)

3.5 in-lb (0.4 N-m)

Temperature (operating)

-20 °C to +70 °C

-20 °C to +70 °C

-20 °C to +70 °C

Temperature (storage)

-40 °C to +85 °C

-40 °C to +85 °C

-40 °C to +85 °C

Relative Humidity
(non-condensing)

5-95%

5-95%

5-95%

MTBF (minimum, 25 °C)

1.2 Mhrs

1.2 Mhrs

1.2 Mhrs

Agency Approvals

UL/cUL (Class 1, Div 2)a; CE: ATEX (Category 3, Zone 2) and RoHS; DFARS; CB Scheme; UKCA

Warranty

Lifetime

Lifetime

Lifetime

a. For use in hazardous locations, equipment must be mounted in an enclosure that meets the requirements of the National Electrical Code, ANSI/NFPA 70, and ANSI/ISA-61010-1 (82.02.01).

Opto Products are ideal for OEMs and machine designers, process control, machine monitoring, power and energy monitoring, predictive maintenance, remote installations like water-wastewater and oil & gas, SCADA, and industrial internet of things applications.

groov Analog Voltage Input Module Data Sheet

groov analog voltage input modules are part of Opto 22's groov EPIC System. This document includes descriptions, specifications, and wiring and dimensional diagrams for the following part numbers:

groov I/O Modules Firmware Release Notes

This document lists the latest updates to the firmware for groov I/O modules. It includes information on new features, enhancements, and bug fixes.

List of groov I/O module firmware download pages

Note: This document was formerly called a readme. The name was changed to more accurately describe its content.

UKCA Declaration of Conformity (groov EPIC and groov RIO)

This document is the Manufacturer's Declaration of Conformity for groov EPIC and groov RIO and their accessories, in accordance with the rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

ATEX Letter of Conformity for groov EPIC

This ATEX Letter of Conformity is provided to support CE Declaration of Conformity (groov EPIC and groov RIO), form 2261.

Declaration of Conformity (groov EPIC and groov RIO)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

GRV-IV-24 Module Firmware

This download contains current firmware for the GRV-IV-24 module. For a list of new features, enhancements, and bug fixes included in this firmware, see the groov I/O Modules Firmware Release Notes.

You can download the previous version of the firmware by clicking on this link: 1.3b, 1.3a, 1.0l

CAD Drawing: groov I/O Module

This ZIP file includes drawings in a variety of file formats (pdf, dwg, stp) that apply to all groov I/O modules.

Note: These drawings do not apply to groov RIO modules.

CAD Drawings: groov EPIC and groov RIO I/O wiring

This ZIP file contains I/O wiring diagrams for groov EPIC I/O modules and groov RIO models, in DWG format.

Accuracy vs Resolution

What's the difference between accuracy and resolution in analog I/O specifications? Try your own specs in the calculator.