AC discrete input, 24 channels, 180-280 VAC, on/off state only

Production Specification

Part of the groov EPIC® system, the GRV-IACHVS-24 digital input module can sense status from up to 24 devices such as pumps, fans, and motors that use a 180–280 VAC signal. This module provides only on or off sensing, offering a lower cost option for projects with simple requirements. The module cover includes an LED that indicates status and a touch-sensitive pad. Touch the pad and the groov EPIC processor displays information about the module, including specifications and a wiring diagram.

The GRV-IACHVS-24 module mounts on a groov EPIC® chassis alongside other digital, analog, and serial I/O modules, to provide the mix of signals you need at any location.

NOTE: If your application requires a larger set of features (latching, totalization, and so on) in addition to on/off status, see the GRV-IACHV-24. If you require channel-to-channel isolation, see the GRV-IACIHV-12.

All groov I/O modules are UL/cUL listed and compliant with the ATEX, Low Voltage, and EMC CE and UKCA directives. Each module is factory tested twice before shipment and most modules are guaranteed for life.
Feature GRV-IACHV-24 GRV-IACHVS-24 GRV-IACIHV-12 GRV-IACIHVS-12
Number of Channels 24 24 12 12
Channel-to-Channel Isolation    
Counting    
Frequency Measurement    
On/Off Latching    
On/Off State
On/Off Totalization    
Period Measurement    
Pulse Measurement    
Quality Indication        
 
Specification GRV-IACHV-24 GRV-IACHVS-24 GRV-IACIHV-12 GRV-IACIHVS-12
Nominal Input Voltage Range (RMS) 180–280 VAC / VDC 180–280 VAC / VDC 180–280 VAC / VDC 180–280 VAC / VDC
Turn-on Voltage 180 VAC / VDC 180 VAC / VDC 180 VAC / VDC 180 VAC / VDC
Turn-off Voltage 35 VAC / VDC 35 VAC / VDC 35 VAC / VDC 35 VAC / VDC
Input Impedance (±5%) 532 kOhms 532 kOhms 271 kOhms 271 kOhms
Operating Frequency 40 Hz to 400 Hz or DC 40 Hz to 400 Hz or DC 40 Hz to 400 Hz or DC 40 Hz to 400 Hz or DC
Turn-on Time (typical) 30 ms at V 30 ms at V 30 ms at V 30 ms at V
Turn-off Time (typical) 30 ms at V 30 ms at V 30 ms at V 30 ms at V
Isolation (field-to-logic) 300 VAC, 1500 V Transient 300 VAC, 1500 V Transient 300 VAC, 1500 V Transient 300 VAC, 1500 V Transient
Isolation (channel-to-channel) N/A N/A 300 VAC working 300 VAC working
Number of Channels 24 24 12 12
Chassis Power Consumption 1.0 W 1.0 W 1.0 W 1.0 W
Minimum groov EPIC Firmware Version 1.0.0 1.0.0 1.0.0 1.0.0
Minimum PAC Project Version 10.0000 10.0000 10.0000 10.0000
Minimum Library Package for CODESYS Version 1.0.0.0 1.0.0.0 1.0.0.0 1.0.0.0
Wire Size 28–14 AWG 28–14 AWG 28–14 AWG 28–14 AWG
Wire Strip Length 0.315–0.354 inches (8–9 mm) 0.315–0.354 inches (8–9 mm) 0.315–0.354 inches (8–9 mm) 0.315–0.354 inches (8–9 mm)
Torque, connector screw 2.5 in-lb (0.28 N-m) 2.5 in-lb (0.28 N-m) 2.5 in-lb (0.28 N-m) 2.5 in-lb (0.28 N-m)
Torque, hold-down screw 3.5 in-lb (0.4 N-m) 3.5 in-lb (0.4 N-m) 3.5 in-lb (0.4 N-m) 3.5 in-lb (0.4 N-m)
Temperature (operating) -20 °C to +70 °C -20 °C to +70 °C -20 °C to +70 °C -20 °C to +70 °C
Temperature (storage) -40 °C to +85 °C -40 °C to +85 °C -40 °C to +85 °C -40 °C to +85 °C
Relative Humidity (non-condensing) 5–95% 5–95% 5–95% 5–95%
MTBF (minimum, 25°C) 1.2 Mhrs 1.2 Mhrs 1.2 Mhrs 1.2 Mhrs
Agency Approvals UL/cUL (Class 1 Div. 2)a; CE: ATEX (Category 3, Zone 2) and RoHS; DFARS; CB Scheme; UKCA
Warranty Lifetime Lifetime Lifetime Lifetime

a For use in hazardous locations, equipment must be mounted in an enclosure that meets the requirements of the National Electrical Code, ANSI/NFPA 70, and ANSI/ISA-61010-1 (82.02.01).
 

groov 180-280 VAC Input Modules Data Sheet

groov® 180-280 VAC input modules are part of Opto 22's groov EPIC® System. This document includes descriptions, specifications, and wiring and dimensional diagrams for the following part numbers:

groov I/O Modules Firmware Release Notes

This document lists the latest updates to the firmware for groov I/O modules. It includes information on new features, enhancements, and bug fixes.

List of groov I/O module firmware download pages

Note: This document was formerly called a readme. The name was changed to more accurately describe its content.

UKCA Declaration of Conformity (groov EPIC and groov RIO)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with the rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

ATEX Letter of Conformity for groov EPIC

This ATEX Letter of Conformity is provided to support CE Declaration of Conformity (groov EPIC and groov RIO), form 2261.

Declaration of Conformity (groov EPIC and groov RIO)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

groov simple I/O modules firmware

This download contains current firmware for the following modules, also called groov simple I/O modules:

  • GRV-IACHVS-24
  • GRV-IACIHVS-12
  • GRV-IACS-24
  • GRV-IACIS-12
  • GRV-IDCS-24
  • GRV-IDCIS-12
  • GRV-OACS-12
  • GRV-OACIS-12
  • GRV-IACDCTTLS-24
  • GRV-ODCIS-12
  • GRV-OMRIS-8
For a list of bug fixes and enhancements included in this firmware, see the groov I/O Modules Firmware Release Notes document.

You can download previous versions of the firmware by clicking on the following links: 1.6e, 1.4b

GRV-IACHVS-24 Module Firmware

This download contains current firmware for the GRV-IACHVS-24 module. For a list of bug fixes and enhancements included in this firmware, see the groov I/O Modules Firmware Release Notes.

You can download the previous version of the firmware by clicking on this link: 1.6e1.4b

CAD Drawing: groov I/O Module

This ZIP file includes drawings in a variety of file formats (pdf, dwg, stp) that apply to all groov I/O modules.

Note: These drawings do not apply to groov RIO modules.

CAD Drawings: groov EPIC and groov RIO I/O wiring

This ZIP file contains I/O wiring diagrams for groov EPIC I/O modules and groov RIO models, in DWG format.

No videos or demos are available for this product.