$64.00 (USA and Canada only)
Optical Isolation Input to Output
4,000 V
Turn-on Time
½ cycle maximum
Turn-off Time
Operating Frequency
25 to 65 Hz (operates at 400 Hz with six times off-state leakage)
Coupling Capacitance Input to Output
8 pF maximum
DV/DT Off-state
200 volts per microsecond
DV/DT Commutating
Snubbed for rated current at 0.5 power factor
240D3
240D10
240Di10
240D25
240Di25
240D45
240Di45
Nominal AC Line Voltage
240
Nominal Current Rating (Amps)
3*
10*
25*
45*
1 cycle Surge (Amps) Peak
85
110
250
650
Nominal Signal Input Resistance (Ohms)
1000
730
Signal Pick-up Voltage
3VDC (32V allowed)
Signal Drop-out Voltage
1 VDC
Peak Repetitive Voltage Maximum
600
Maximum Output Voltage Drop
1.6 volts
Off-State Leakage (mA) Maximum
5 mA
14 mA
Operating Voltage Range (Volts AC)
24–280
12–280
I2t Rating t=8.3 (ms)
30
50
1750
Isolation Voltage
4,000VRMS
θjc** (°C/Watt)
11
1.3
1.2
0.67
Dissipation (Watts/Amp)
1.7
1.6
0.9
Notes: * Ambient temperature will affect the current rating. For details, see the Thermal Ratings charts in the Solid State Relays Data Sheet (form 0859). ** θjc = Thermal resistance from internal junction to base. Maximum internal junction temperature is 110 °C.
A quick overview of Opto 22 solid-state relays (SSRs).
Opto 22 provides a full range of reliable solid-state relays (SSR). This data sheet includes descriptions, specifications, dimensional drawings, and application information.
This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with the rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.
This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.
This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.
This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.
This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with the mentioned European, international and/or national standards and regulations.
$77.00