Production Specification

The 120D25 is a DC-controlled Power Series relay that switches 120 VAC at up to 25 A.

Power Series relays provide 4000 volts of isolation between input and output, and offer zero-voltage turn-on and zero-current turn-off. They are UL and CSA recognized and are a CE component, UKCA certified.

Lots of information on choosing and using SSRs can be found in the SSR data sheet. Also see the Manufacturers' part number cross-reference list.

This SSR carries a lifetime warranty.

NOTE: We do not recommend mounting the terminal side of the SSR to a flat PCB (printed circuit board) or other flat surface, because there may be some variation in terminal height from one terminal to another and from one SSR to another. Use the MP or P series SSRs for PCB mounting.

Optical Isolation Input to Output

4,000 V

Turn-on Time

½ cycle maximum

Turn-off Time

½ cycle maximum

Operating Frequency

25 to 65 Hz (operates at 400 Hz with six times
off-state leakage)

Coupling Capacitance Input to Output

8 pF maximum

DV/DT Off-state

200 volts per microsecond

DV/DT Commutating

Snubbed for rated current at 0.5 power factor

Agency Approvals UL, CSA, RoHS, CE; UKCA

 

 

120D3

120D10

120D25

120D45

Nominal AC Line Voltage

120

120

120

120

Nominal Current Rating
(Amps)

3*

10*

25*

45*

1 cycle Surge (Amps) Peak

85

110

250

650

Nominal Signal Input
Resistance (Ohms)

1000

1000

1000

1000

Signal Pick-up Voltage

3VDC (32V allowed)

3VDC (32V allowed)

3VDC(32V allowed)

3VDC (32V allowed)

Signal Drop-out Voltage

1 VDC

1 VDC

1 VDC

1 VDC

Peak Repetitive Voltage
Maximum

600

600

600

600

Maximum Output
Voltage Drop

1.6 volts

1.6 volts

1.6 volts

1.6 volts

Off-State Leakage
(mA) Maximum

2.5mA

7 mA

7 mA

7 mA

Operating Voltage Range (Volts AC)

12–140

12–140

12–140

12–140

I2t Rating t=8.3 (ms)

30

50

250

1750

Isolation Voltage

4,000VRMS

4,000VRMS

4,000VRMS

4,000VRMS

θjc** (°C/Watt)

11

1.3

1.2

0.67

Dissipation (Watts/Amp)

1.7

1.6

1.3

0.9

Notes:
* Ambient temperature will affect the current rating. For details, see the Thermal Ratings charts in the Solid State Relays Data Sheet (form 0859).
** θjc = Thermal resistance from internal junction to base. Maximum internal junction temperature is 110 °C.

Solid-State Relays (SSRs) Data Sheet

Opto 22 provides a full range of reliable solid-state relays (SSR). This data sheet includes descriptions, specifications, dimensional drawings, and application information for these parts:

  • 120A10
  • 120A25
  • 240A10
  • 240A25
  • 240A45
  • 120D3
  • 120D10
  • 120D25
  • 120D45
  • 240D3
  • 240D10
  • 240Di10
  • 240D25
  • 240Di25
  • 240D30-HS [Obsolete]
  • 240D45
  • 240Di45
  • 380D25
  • 380D45
  • 480D10-12
  • 480D15-12
  • 480D25-12
  • 480D25-HS [Obsolete]
  • 480D45-12
  • 575D15-12
  • 575D45-12
  • 575D30-HS  [Obsolete]
  • 575Di45-12
  • DC60P or DC60MP
  • DC200P or DC200MP
  • DC60S-3
  • DC60S-5
  • MP120D2 or P120D2 [Obsolete]
  • MP120D4 or P120D4
  • MP240D2 or P240D2
  • MP240D4 or P240D4
  • MP380D4
  • SAFETY COVER
  • SSR-HS
  • SSR-THERMOPAD
  • Z120D10
  • Z240D10

Opto 22 SSR Overview

A quick overview of Opto 22 solid-state relays (SSRs).

UKCA Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with EMC, LVD, and RoHS rules, regulations and standards of the United Kingdom. The models cited have been tested to the essential requirements listed in the Standards section, and fully comply with the legislation as listed in UK Legislation section.

Declaration of Conformity (EMC, LVD, RoHS)

This document is the Manufacturer's Declaration of Conformity for the products listed herein, in accordance with European, international, and/or national standards and regulations.

Opto 22 RoHS 3 Statement of Compliance - Restriction of Hazardous Substances

This document is a statement of compliance with the EU Directive 2015/863/EU, Restriction of Hazardous Substances (RoHS 3). This document lists Opto 22 products that comply with the substance restrictions of the RoHS 3 directive.

Solid State Relay Cross-Reference Product List

Guaranteed-for-life Opto 22 solid state relays can often be substituted for other manufacturers' relays. This technical note lists part number matches and notes differences with other manufacturers' products.

For more information on SSRs, see Form 0859, Solid State Relays Data Sheet.

CSA Approval Document

This document lists all Opto 22 part numbers that have the Canadian Standards Association (CSA) approval.

UL Approval Document

This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.

CE Declaration: Component

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/30/EU, but may not include the CE marking due to limitations of component size and/or shape.

CE Declaration: Low Voltage

This document is the Manufacturer's Declaration for the listed products as mentioned in the attachment - to which this confirmation refers - that they are in accordance with Directive 2014/35/EU.

No downloads are available for this product.
No videos or demos are available for this product.