GRV-IDCIS-12
GRV-IDCIS-12
$300.00 (USA and Canada only)
DC discrete input, 12 channels, 10-30 V, channel-to-channel isolation, on/off status only
The GRV-IDCIS-12 digital DC input module senses the on or off status of 10–30 VDC input devices such as proximity switches, push buttons, and auxiliary contacts. The module provides channel-to-channel isolation for its 12 channels. Each channel senses DC input state only, offering a lower cost option for projects with simple requirements.
Part of the groov EPIC® system, the GRV-IDCIS-12 mounts on a groov EPIC® chassis alongside other discrete, analog, and serial groov I/O modules and a GRV-EPIC-PR1 processor.
NOTE: If you project requires additional features, such as latching and totalizing, see the GRV-IDCI-12.
Feature GRV-IDC-24 GRV-IDCS-24 GRV-IDCI-12 GRV-IDCIS-12 GRV-IDCIFQ-12
Number of channels
24
24
12
12
12
Channel-to-channel isolation
x
x
x
On/off state
x
x
x
x
x
On/off latching
x
x
x
Counting
x
x
x
On/off totalization
x
x
x
Frequency measurement
x
x
x
Period measurement
x
x
x
Pulse measurement
x
x
x
Quadrature
x
10–25 VAC
10–30 VDC 2.5–30 VDC
Input Impedance (± 5%) See Note 1. See Note 1. See Note 1. See Note 1. 1.1 K at 5 V,
2.2 K at 12 V,
3.5 K at 24 V
Max. On/Off Freq. (AC Input, 24 VAC, 60 Hz) N/A N/A 20 Hz N/A N/A
Agency Approvals UL/cUL(Class 1 Div. 2) (See Note 2.); CE, ATEX(Category 3, Zone 2), RoHS; DFARS; CB Scheme; UKCA
Note 1: IEC inputs have non-linear impedance. See the tables in the data sheet for typical V-I curves.
Note 2: For use in hazardous locations, equipment must be mounted in an enclosure that meets the requirements of the National Electrical Code, ANSI/NFPA 70, and ANSI/ISA-61010-1 (82.02.01).
GRV-IDCIS-12 Module Firmware
This download contains current firmware for the GRV-IDCIS-12 module. For a list of bug fixes and enhancements included in this firmware, see the groov I/O Modules Firmware Release Notes.
CAD Drawing: groov I/O Module