GRV-IACHV-24
GRV-IACHV-24
$380.00 (USA and Canada only)
AC discrete input, 24 channels, 180-280 VAC
Part of the groov EPIC® system, the GRV-IACHV-24 AC digital input module can sense status from up to 24 devices such as pumps, fans, and motors that use a 180–280 VAC signal. Field devices are isolated from the logic side of the module, but channels are not isolated from each other: they share a common connection inside the module.
The GRV-IACHV-24 module offers a full set of features, including:
  • On/off state
  • On/off latching
  • On/off totalization
  • Frequency measurement
  • Period measurement
  • Pulse measurement
The GRV-IACHV-24 module mounts on a groov EPIC chassis alongside a GRV-EPIC-PR1 processor and other digital, analog, and serial groov I/O modules
NOTE: If your project requires only on and off sensing, see the lower-cost GRV-IACHVS-24 module.
Feature GRV-IACHV-24 GRV-IACHVS-24 GRV-IACIHV-12 GRV-IACIHVS-12
Number of channels 24 24 12 12
Channel-to-channel isolation     x x
On/off state x x x x
On/off latching x   x
On/off totalization x   x
Frequency measurement x   x
Period measurement x   x
Pulse measurement x   x
Specification GRV-IACHV-24 GRV-IACHVS-24 GRV-IACIHV-12 GRV-IACIHVS-12
Nominal Input Voltage Range (RMS) 180–280 VAC 180–280 VAC 180–280 VAC 180–280 VAC
Turn-on Voltage 180 VAC 180 VAC 180 VAC 180 VAC
Turn-off Voltage 35 VAC 35 VAC 35 VAC 35 VAC
Input Impedance (±5%) 532 kOhms 532 kOhms 271 kOhms 271 kOhms
Operating Frequency 40 Hz to 400 Hz 40 Hz to 400 Hz 40 Hz to 400 Hz 40 Hz to 400 Hz
Turn-on Time (typical) 30 ms at V 30 ms at V 30 ms at V 30 ms at V
Turn-off Time (typical) 30 ms at V 30 ms at V 30 ms at V 30 ms at V
Isolation (field-to-logic) 300 VAC, 1500 V Transient 300 VAC, 1500 V Transient 300 VAC, 1500 V Transient 300 VAC, 1500 V Transient
Isolation (channel-to-channel) N/A N/A 300 VAC working 300 VAC working
Number of Channels 24 24 12 12
Chassis Power Consumption 1.0 W 1.0 W 1.0 W 1.0 W
Agency Approvals UL/cUL (Class 1 Div. 2)a; CE, ATEX (Category 3, Zone 2), RoHS; DFARS; CB Scheme; UKCA
groov 180-280 VAC Input Modules Data Sheet
groov® 180-280 VAC input modules are part of Opto 22's groov EPIC® System. This document includes descriptions, specifications, and wiring and dimensional diagrams for the following part numbers:
CAD Drawing: groov I/O Module
GRV-IACHV-24 Module Firmware
This download contains current firmware for the GRV-IACHV-24 module. For a list of bug fixes and enhancements included in this firmware, see the groov I/O Modules Firmware readme document.
You can download the previous version of the firmware by clicking on this link: 1.3b1.3a1.0k